Testing a socket in the middle of a distribution circuit.

Discuss Testing a socket in the middle of a distribution circuit. in the The Welcome Forum area at ElectriciansForums.net

I have a socket in my loft tapped off the garage circuit which is not RCD protected. Shall I do the honourable thing and shoot myself now?
but can the socket be used to supply equipment outdoors? :(
 
but can the socket be used to supply equipment outdoors? :(

Hey up Tel.... he did say it's an outdoor socket ;)

SWA does not need an up front rcd. Change the socket to an rcd socket so this sub main is a continuous feed t the summer house cu OR make it a junction box and run new cable to an outside socket? Whatever is best for the location.
 
Hey up Tel.... he did say it's an outdoor socket ;)

SWA does not need an up front rcd. Change the socket to an rcd socket so this sub main is a continuous feed t the summer house cu OR make it a junction box and run new cable to an outside socket? Whatever is best for the location.
i was referring to Strima's attic socket.
 
Not sure there is a reg saying this can't be done but it brings with it loads of issues such as IP ratings, rcd/rcbos etc.. and discrimination... not sure the part p scams would be too pleased if shown it on a assessment.
 
Not sure there is a reg saying this can't be done but it brings with it loads of issues such as IP ratings, rcd/rcbos etc.. and discrimination... not sure the part p scams would be too pleased if shown it on a assessment.
I don't see 'loads of issues'.

Suppose you have a radial circuit on a 32A MCB supplying a properly IP rated RCD socket, then on to a board in a shed with RCD main switch. Where are the issues?
 
That is exactly what it was. Exactly. However, following the general consensus that it was somewhat unconventional, I have changed the socket for a junction. It's part of an application to join Elecsa.....so I want limited debate.

Thanks everyone for your input....these forums really are an incredible resource. I guess it helps you commentators keep it all fresh in your mind. Cheers Kelsall
 
^^^ Please for the love of God (and our entertainment) put in an RCD socket and let the assessor pull you on it..... then ask him to give you the reg numbers that it goes against??????
 
i was referring to Strima's attic socket.

Sorry bud, been off the forums for a while and I missed what you were on about. I'm a bit rusty

download (7).jpg
 

Reply to Testing a socket in the middle of a distribution circuit. in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock