To Build a Double RCB Consumer unit

Discuss To Build a Double RCB Consumer unit in the Australia area at ElectriciansForums.net

S

spike47

100_2022.jpgHi there
Attached is a photo of my CU , it is a split unit , 80amp MCB main switch left and a 60amp RCB on the right , I want to build this to a Double RCB unit , but has you can see in the picture it has only 2 Neutral terminal bars , any info has to how I can fit another Neutral bar for the second RCB switch , I had thought about reducing the lengh of the earth Terminal !! .

cheers


spike
 
Last edited by a moderator:
You could get it replaced for a 17th edition board, which would have been built with dual rcd capability in mind. It could incorporate that shower unit to the right as well, so would be tidier.
 
As Geoff said you can reconfigure the existing to use the non rcd neutral bar as an RCD bar, jst take the existing neutral connection to the tops of the RCDs and and tail out from the added one to the existing. I hope that makes sense :D
 

Reply to To Build a Double RCB Consumer unit in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock