Hoping someone might be able to help. I’ve seen an ‘adaptor’ that allows 2 test leads to run from one port of an MFT (doing IR test). But, can’t find anywhere to buy it. Anyone know where I could get one from?
 
Erm, why would you wat to do that is the obvious question.

The idea of ir testing is to show the resistance between 2 items, if you add a 3rd in to the equation then you have the possibility of joining 2 things that are at different potential and destroying a set of leads amongst the other risks.
 
Hoping someone might be able to help. I’ve seen an ‘adaptor’ that allows 2 test leads to run from one port of an MFT (doing IR test). But, can’t find anywhere to buy it. Anyone know where I could get one from?
The makers of the MFT?
 
Erm, why would you wat to do that is the obvious question.

The idea of ir testing is to show the resistance between 2 items, if you add a 3rd in to the equation then you have the possibility of joining 2 things that are at different potential and destroying a set of leads amongst the other risks.
Surely, you understand that let’s say you link L&N together and test with earth, as you’re passing 500v down both L&N then the potential difference is zero. So, no you would not destroy the leads.
 
Hoping someone might be able to help. I’ve seen an ‘adaptor’ that allows 2 test leads to run from one port of an MFT (doing IR test). But, can’t find anywhere to buy it. Anyone know where I could get one from?
IR test is 2 lead test anyways.....can’t see how joining em is gonna achieve anything ?? Kewtech do a piggy back lead for joining neutral and earth when performing Ze high current loop test....is that what you are referring to?
 
IR test is 2 lead test anyways.....can’t see how joining em is gonna achieve anything ?? Kewtech do a piggy back lead for joining neutral and earth when performing Ze high current loop test....is that what you are referring to?
I get that it’s a two lead test. But watching a GSH video where they do IR test, rather than using croc clip to L&N they had this funky looking piggyback lead.
 
Do you mean like this?
76A761F0-49E6-4976-8724-FD21F5ABB9A1.jpeg
 
I can't understand why everyone is so confused. Sometimes you want to do some test or another from A + B to C. For an IR test that might be L+N to E, or L1 + L2 + L3 to E or whatever, which if you have stackable test leads, you can achieve by putting one clip on each conductor and stacking / piggybacking the leads if they are stackable. It reduces the number of things that might come apart or ping off during the test, vs jumpering with separate croc clip leads. In electronics lab work, joining, branching and daisy-chaining test leads is normal so most bench test leads have a piggyback socket.

I keep a set of touchproof stackable leads and probes in the testing kit to make up whatever configuration is required. They are only for dead tests though as they are not CAT III rated.
 
Ah, Lucien's post has helped. The wording of the question made me think the OP was trying to do some sort of different test by using both ports of the MFT.
 
I can't understand why everyone is so confused. Sometimes you want to do some test or another from A + B to C. For an IR test that might be L+N to E, or L1 + L2 + L3 to E or whatever, which if you have stackable test leads, you can achieve by putting one clip on each conductor and stacking / piggybacking the leads if they are stackable. It reduces the number of things that might come apart or ping off during the test, vs jumpering with separate croc clip leads. In electronics lab work, joining, branching and daisy-chaining test leads is normal so most bench test leads have a piggyback socket.

I keep a set of touchproof stackable leads and probes in the testing kit to make up whatever configuration is required. They are only for dead tests though as they are not CAT III rated.
Oh yeah, that's a good idea :D
 
I was always under the impression that if you individually test L to E, and N to E, without joining them together, you basically do the same test, just without the hassle of having to use piggyback leads or disconnect stuff?
 
But if there are hidden loads on an existing circuit being tested for an EICR, not joining L & N together could inadvertently apply 500V across the load and cause damage. Best to test both to earth at once if unsure.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Keighley
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Two test leads, one port
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
Haworth,
Last reply from
Lucien Nunes,
Replies
31
Views
5,422

Advert

Back
Top