Mike the mx allowed is 80% of the tabulated value though. Not nitpicking, discussing
really?
Discuss type C Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net
Mike the mx allowed is 80% of the tabulated value though. Not nitpicking, discussing
Out of interest trev we allow 85% on EICR's, sometimes upto 90% if previous results are taken into account and show stable readings. The 100% value is the max allowable I believe. But you would always use 80% for design and installation.Mike the mx allowed is 80% of the tabulated value though. Not nitpicking, discussing
Aye, that's what I was getting atyou would always use 80% for design and installation.
See post 23 mate. Sorry, misplaced me thinking heedreally?
look...I've done the same, hopefully we will be rid of him soon
The answer is 1.44 IMO, I don't write 80% values down on sheets myself, it asks for maximum values does it not?
yes....the correction factor would be irrelevent100% agree! If the question is asking for the MAXIMUM allowable value then the answer should be the MAXIMUM allowable value, not the maximum allowable value minus 20%???
the 4 possible answers I have are as followers
A. 0.69
B. 0.2
C.1.15
D. 0.4
I think 0.4ohms. The question relates to reduced low voltage, which is a maximum of 63.5V line to earth. So, taking 1.44ohms for instantaneous operation at 230V line to earth, the value for 63.5V will be 1.44/230, x 63.5, =0.4ohms. Obviously, if the supply is lower than the maximum for reduced LV (not stated) then a lower Zs will be required. (Apologies for no line breaks.)the 4 possible answers I have are as followers
A. 0.69
B. 0.2
C.1.15
D. 0.4
I think 0.4ohms. The question relates to reduced low voltage, which is a maximum of 63.5V line to earth. So, taking 1.44ohms for instantaneous operation at 230V line to earth, the value for 63.5V will be 1.44/230, x 63.5, =0.4ohms. Obviously, if the supply is lower than the maximum for reduced LV (not stated) then a lower Zs will be required. (Apologies for no line breaks.)
Reply to type C Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net