Passed My 2392-10 Certificate / Fundamental Inspection , Testing & Initial Verification :
Have a lot off 2391-10 stuff , when I get a chance I’ll down load them ,
Jason I’ll need to use a new folder Amberleaf , how will I word it !!!!!!!!!!!!!!!!!!!!!!!!!!!!!
Testing –
The Obtaining and Recording of the Installations ( Psc ) & ( Ze ) Details :
When Obtaining the Values of either the Psc & Ze at the Origin of the Installation three Methods appear to be Acceptable :
(1) By Enquiry : Usually given upon request to the local Regional Electricity Board , it is common practice for them to quote
A maximum value “ this usually being 16kA for the Prospective Short Circuit Current and earth loop values of 0.35Ω for TN-C-S 0.8Ω for a TN-S system , O.S.G. p-11
(2) By Calculation :
The Designer , using information given , with regard to cable sizing , length of run from the sub-station , etc , can calculate the (PSC ) & the Phase Earth Loop Impedance at the Origin of the Installation ,
(3) By Direct Measurement :
Using a Instrument a direct measurement can be made for the ( PSCC ) ↔ ( PFC ) & ( Ze ) of the Installation
at the Supply intake Terminals ,
* Test results do not specify whether the actual recorded instrument reading is that of a ( Phase / Neutral or a ( Phase / Phase short circuit ,
Although the worst scenario is a short circuit fault across the three phase it appears that a Phase / Neutral measurement is acceptable :
“ Measurement of the Prospective Earth Fault Current “
To measure the Earth Fault Current as a direct reading in Amps , the Instrument ( Neutral Lead can be Connected to the Earth Block )
with the Instrument still set on the current range what will now be measured is the Prospective Earth Fault Current ,
* ( Psc ) range kA ,
By Using this method it saves you having to divide the Earth Loop Impedance reading previously obtained into the supply voltage to
obtain the Earth Fault Current ,
Prospective Short Circuit Current to be measured and recorded , but where the Prospective Earth Fault Current exceeds that of the Short Circuit Current then this Value should be recorded in its place ,
the value of whichever is the Greater should be recorded on the Certificate as the Prospective Fault Current ( Pfc )
“ Measurement of the Short Circuit Current “
“ Range kA “
The test is made using a dedicated ( Psc ) Instrument connected as ( Line & Neutral )
( Most Earth Loop Impedance Instruments incorporate the facility for the measurement of the Phase-Neutral Prospective Short Circuit Current ,
The Protective Devices at the Point of Test must have a Short Circuit Rating in Excess of the reading taken ,
( the Exemptions from this Requirement are when MCBs etc. are used for Overload Protection and BS-1361 or BS-88
Protective devices with suitable operating Characteristics { POSITIONED on the SUPPLY SIDE ϟϟ }
Contractors will Only have Instruments capable of Psc measurement’s at 230V , so a problem will arise on Three Phase systems where a
Ph – Ph –Ph measurement is required , if a 3-Phase measurement is required it has unfortunately become common practice to multiply
The Single Phase recorded measurement by a factor of ( Ѷ 3 )
On Three Phase systems it should be policy to measure and record both the Three Phase Short Circuit Current ( Ph-Ph-Ph ) and
Single Phase Short Circuit Fault Current ,
( Unfortunately Obtaining the ( Ph-Ph-Ph ) Short Circuit Current is easier said than done ,
The Earth Fault Loop Impedance ( Zs ) is made up of the Impedance of the Consumers Phase & Protective Conductors ( R1 and R2 )
Respectively , and the Impedance external to the Installation ( Ze ) Impedance of the Supply ,
As the value of ( Ze ) will be obtained from the Electricity Company for the Initial assessment of the Installation ,
The maximum Impedance allowed for the Phase & Protective Conductors can be determined from :
( Zs + Ze + R1 + R2 )
Radial Circuit :
13Amp Immersion heater circuit protected by a Type B 16amp MCB , wired in 2.5mm2 PVC sheathed cable with a 1.5mm2 CPC
Supplied from 230 volt single phase TN-C-S system , what is the maximum length of run ? ( mV 19.51 x A 16 = 31.2m ) 2391 **
If = Uo / Zs : ( 230v Phase to Earth ) 230 ÷ 0.93Ω = 247A
Zs : R1 , 0.5Ω + R2 , 0.43Ω = 0.93Ω


Passed My 2392-10 Certificate / Fundamental Inspection , Testing & Initial Verification :
Have a lot off 2391-10 stuff , when I get a chance I’ll down load them ,

Jason I’ll need to use a new folder Amberleaf , how will I word it !!!!!!!!!!!!!!!!!!!!!!!!!!!!!

Testing –

The Obtaining and Recording of the Installations ( Psc ) & ( Ze ) Details :
When Obtaining the Values of either the Psc & Ze at the Origin of the Installation three Methods appear to be Acceptable :
(1) By Enquiry : Usually given upon request to the local Regional Electricity Board , it is common practice for them to quote
A maximum value “ this usually being 16kA for the Prospective Short Circuit Current and earth loop values of 0.35Ω for TN-C-S 0.8Ω for a TN-S system , O.S.G. p-11
(2) By Calculation :
The Designer , using information given , with regard to cable sizing , length of run from the sub-station , etc , can calculate the (PSC ) & the Phase Earth Loop Impedance at the Origin of the Installation ,
(3) By Direct Measurement :
Using a Instrument a direct measurement can be made for the ( PSCC ) ↔ ( PFC ) & ( Ze ) of the Installation
at the Supply intake Terminals ,
* Test results do not specify whether the actual recorded instrument reading is that of a ( Phase / Neutral or a ( Phase / Phase short circuit ,
Although the worst scenario is a short circuit fault across the three phase it appears that a Phase / Neutral measurement is acceptable :
“ Measurement of the Prospective Earth Fault Current “
To measure the Earth Fault Current as a direct reading in Amps , the Instrument ( Neutral Lead can be Connected to the Earth Block )
with the Instrument still set on the current range what will now be measured is the Prospective Earth Fault Current ,
* ( Psc ) range kA ,
By Using this method it saves you having to divide the Earth Loop Impedance reading previously obtained into the supply voltage to
obtain the Earth Fault Current ,
Prospective Short Circuit Current to be measured and recorded , but where the Prospective Earth Fault Current exceeds that of the Short Circuit Current then this Value should be recorded in its place ,
the value of whichever is the Greater should be recorded on the Certificate as the Prospective Fault Current ( Pfc )
“ Measurement of the Short Circuit Current “
“ Range kA “
The test is made using a dedicated ( Psc ) Instrument connected as ( Line & Neutral )
( Most Earth Loop Impedance Instruments incorporate the facility for the measurement of the Phase-Neutral Prospective Short Circuit Current ,
The Protective Devices at the Point of Test must have a Short Circuit Rating in Excess of the reading taken ,
( the Exemptions from this Requirement are when MCBs etc. are used for Overload Protection and BS-1361 or BS-88
Protective devices with suitable operating Characteristics { POSITIONED on the SUPPLY SIDE ϟϟ }
Contractors will Only have Instruments capable of Psc measurement’s at 230V , so a problem will arise on Three Phase systems where a
Ph – Ph –Ph measurement is required , if a 3-Phase measurement is required it has unfortunately become common practice to multiply
The Single Phase recorded measurement by a factor of ( Ѷ 3 )
On Three Phase systems it should be policy to measure and record both the Three Phase Short Circuit Current ( Ph-Ph-Ph ) and
Single Phase Short Circuit Fault Current ,
( Unfortunately Obtaining the ( Ph-Ph-Ph ) Short Circuit Current is easier said than done ,
The Earth Fault Loop Impedance ( Zs ) is made up of the Impedance of the Consumers Phase & Protective Conductors ( R1 and R2 )
Respectively , and the Impedance external to the Installation ( Ze ) Impedance of the Supply ,
As the value of ( Ze ) will be obtained from the Electricity Company for the Initial assessment of the Installation ,
The maximum Impedance allowed for the Phase & Protective Conductors can be determined from :
( Zs + Ze + R1 + R2 )
Radial Circuit :
13Amp Immersion heater circuit protected by a Type B 16amp MCB , wired in 2.5mm2 PVC sheathed cable with a 1.5mm2 CPC
Supplied from 230 volt single phase TN-C-S system , what is the maximum length of run ? ( mV 19.51 x A 16 = 31.2m ) 2391 **
If = Uo / Zs : ( 230v Phase to Earth ) 230 ÷ 0.93Ω = 247A
Zs : R1 , 0.5Ω + R2 , 0.43Ω = 0.93Ω
Last edited by a moderator:

The principle of SELV is that by reducing the voltage to 50V or below the risk of electric shock is reduced and additionally with SELV the equipment supplied through a BS-EN 61558-1 transformer will have no return path to the source given that there is no connection to earth. Regulations within BS 7671 regarding the use of SELV as a protective measure can be found in Chapter 41 specifically regulation 414.1 / 414.4.5