Voltage on fittings in bathroom

Discuss Voltage on fittings in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom above - and got a shock from the bathroom tap (and his 'pen glowed on everything')

Turned up to check and, sure enough, voltage of 16V AC showing on the (plumbed) towel radiator, the basin tap and the bath taps - but not on other pipework. This disappeared when the socket circuit was isolated.

Kewtech pen more or less lit up anywhere in the bathroom, including the walls - and the carpet of the adjacent room!

There was no supplementary bonding in place, and a late 60s metal Wylex board with plug in MCBs, There was gas bonding, but no water bonding - however the incoming water was seemingly in some sort of plastic (Plumber didn't know it's name but has seen it before used in properties of this age)

My first thoughts was that perhaps a junction box was sitting in water...

However the plumber struggled to find any noticeable leak, other than a fairly small but constant run from the shower screen when shower was on...

Lots of head scratching later and discovered the problem, but not one I would have guessed at.

Finally cut a hole in the kitchen ceiling below, to find a damp patch (but not floods of water) right where the cabling ran up in the stud wall to a socket in the adjacent bedroom.

Located the relevant socket in the back of a built in chest of drawers, and the bottom wooden joist of the stud wall was sopping wet. However, the socket itself was bone dry with no sign of water damage. Also no sign of damage to the cable sheath where it ran through the wet wood.

However, it it looks like in some way the flow from the shower had run under the tiles and soaked the joist of the stud wall opposite, enough to allow current to transfer to the heating pipes that also ran through the wall.

This then seemingly transferred to the radiator, and all the other metal fittings in the bathroom.

Interestingly, the basin tap and the radiator were both connected with short plastic tails to copper - I can only assume that the water itself was conductive enough to allow enough of a current to give a noticeable reading. Does show that short 'insulating' pieces don't negate the need for bonding.

Pulling the cabling down into the ceiling below and reconnecting it removed the stray voltage so that clearly was the problem. Whether the leak was resolved or not is fortunately down to the plumber!

It was an emergency job with no warning after a long week, so my brain wasn't fully in gear, but it has raised some interesting issues for me...

My initial thought is that supplementary bonding the pipes in the adjacent boiler cupboard (which should have been done at some point since there is no RCD) would have made this safer, but I'm actually not 100% on that in this particular case...

Since the incoming water is actually in plastic, under current Regs there would be no need for equipotential bonding it - and had supplementary bonding been in place, it's possible that this voltage would have been transferred to the rest of the house, since I imagine the ~16V would not have been enough to trip the MCB.

Am I right in suspecting that?

The best protection would obviously be RCD protection, but it's interesting to note that the circuit that caused the issue in this case is not a bathroom one or even one that ran through a bathroom, so would not necessarily be considered on an EICR as a C2 due to lack of RCD protection (because it covered downstairs sockets in this case it would, but if it had only been upstairs sockets then I'd have considered it a C3.)

I guess it's also possible that the current was below 30mA, but I experienced it myself and it was definitely more than a static tingle.

I've raised the topic of a new consumer unit with the elderly houseowner and she seemed keen so hopefully we will resolve that at some point. And the plumber will ensure that the leak is sorted too.

Is this a situation that others have run into? Am I missing something blindingly obvious?

The leak seems to have been generated by the British Gas man servicing the boiler in the morning, and possibly running the shower for a while (which the homeowner rarely uses) and causing the leak this time, but there were tide marks on the stud wallpaper that suggested it had happened before....

Pics to follow if anyone's interested....
 
I think you're missing that the first picture shows two off T&E going up through the hole, then the next picture shows one cable in the socket back box. I agree, the two white lines below and to the right of the socket do look like paint runs.

I can't help thinking there's a joint in that wall, and it's "not been made very well". Or even, that there's a nail through a cable providing a path through the insulation to make the timber live. In terms of conductivity, it's dissolved salts that make water conductive - and there'll be all sorts naturally in the timber, plus plenty of plaster dust etc from construction. As pointed out, it won't be a very low resistance, but it doesn't need to be to give a tingle.
Westward is right - in the picture I'd already pulled the two grey (Imperial) T&E cables down into the ceiling below, so there were no cables left in this wall - or at least none that were visible or could possibly be running anywhere....

The little cable left in the back box is the original earth strapper with green sleeving. The white flexes to the front are an extension lead that was plugged in, and the aerial lead to a TV on top of the chest of drawers. There's absolutely nothing powered in the bathroom other than the ceiling light, with external switch....

There was nothing to suggest there should be another joint in this wall, at least on the socket circuit involved - plumber checked in the loft to ensure there were no leaks from above. There is a switch wire to the bedroom light, but the stray voltages only occurred with the socket circuit on.

It is possible that there was a junction box somewhere else under the floor, but with a ply floor no easy way to confirm it and beyond the reach of the access camera the plumber had handy....

So everything at the time pointed to it being this socket - but looking at it on paper I'd not think it was either!

It was an original MK single socket (vertical screws), so its possible that it had failed in some way that energised the back box, but the box was not damp to the touch and there was no sign of moisture behind the socket. The wall seemed mostly dry at that point, though there could well be the dissolved salts/plaster that could still conduct some...

The socket appeared in good condition too for its age...

If I do go back to change the CU I'll certainly be giving this circuit a much more thorough investigation - and wouldn't reinstate that socket without a lot more work involved on the wall.

Her insurance company will likely be involved so we'll see what comes from it....
 
I got failed insulation readings between conductors and wall once. found the culprit to be a nail through the skirting board. Amazing how conductive building materials can be!
I would check the cable to make sure it's legit as I've come across fake cable before where the insulation doesn't stop water (Sorry, Lucien Nunes - I still have your sample here on my bookcase. I'll get round to sending it to you one day lol)
 
If there was no water or damp in the socket then I suspect there's possibly still a damaged cable, cable with a screw or nail in or junction box somewhere any or all of which have water around them.

There's a path from Live via water to tap / radiator somewhere.
OP wouldn't trust a pen / volt stick if I were you a very misleading tester imo,
 
OP wouldn't trust a pen / volt stick if I were you a very misleading tester imo,
No sane person 'trusts' a Voltstick for anything, other than if it lights up when a circuit should be dead, it means that something is not as expected, and you should proceed with extreme caution.
For this reason alone, they are invaluable.
 

Reply to Voltage on fittings in bathroom in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock