Hi Guys

Just a word of warning to you all. I have been working on an industrial site that has the old style wylex 3-phase DB's (nothing wrong with them). Whilst isolating circuits I have noticed that some MCBS are NOT disconnecting the supply when in the off position :eek:. Out of the 20 odd breakers 8 have this problem!! It may be an isolated case but I think its worth getting a heads up on.

James :)
 
No probs guys, i now have to check 40 other buildings to see if this is a common fault :(.

P.S. I need to get some photos of the installs, some lighting circuits are on 30a mcbs!! Its even more shocking when you know who the installation contractor was!
 
Wylex isn't the only breed of breakers with this fault. Damp atmosphere and the fact that the things can be in the ON position for years without ever being turned off messes up a lot of them. Ones I've come accross didn't open when turned off but functioned correctly when O/L tripped. I spent years working on live circuits so never assumed anything was off. One advantage of fuses over breakers is, seeing is believing.
Came across many an isolator below a board which wasn't the board isolated.:eek: Makes for an exciting life.:cool:
 
well we've found a few more, around another 50 :eek:. I am asuming that the breakers have been turned off, the periodic inspection is only 3 years old on most of these buildings.............Me thinks someone didn't do there job right!!:rolleyes:
 
well we've found a few more, around another 50 :eek:. I am asuming that the breakers have been turned off, the periodic inspection is only 3 years old on most of these buildings.............Me thinks someone didn't do there job right!!:rolleyes:

Sounds very scarey and I'm surprised that this hasn't come to light before.Are they all rated the same
ampage? possibly a bad batch? or maybe ring circuits supplied from 2 separate breakers?Sounds unbelievable sorry.:(
 
well we've found a few more, around another 50 :eek:. I am asuming that the breakers have been turned off, the periodic inspection is only 3 years old on most of these buildings.............Me thinks someone didn't do there job right!!:rolleyes:


Is there a possibility that these are groups of single pole breakers (instead of 3P) being used to feed motor circuits and your getting a back feed through the other phases of a motor or similar.

Periodics are only as reliable as the outfit who do them. No matter whose name is on the ticket, be wary, after all It's you who'll get your fingers burnt. Far be it from me to say that company entertainment/ lunches/bar bills can go a long way in getting certs for all sorts of things.
 
so far these are all SP MCBS feeding either ring or radial circuits, i have disconected the load from them to check that it wasn't a back feed. The breakers vary in ratings as well:(
 

Reply to WARNING old Style Wylex Breakers (not Plug ins) in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Seems to be my month for finding odd bodges by supposed professionals. Installing an external socket in a shed today at a park home (non-mobile...
Replies
23
Views
4K
Hi All, I stumbled across this site whilst looking for help regarding old 5 amp lighting circuits and thought that this would be the perfect...
Replies
11
Views
2K
extension re wire, with 15 way wylex consumer unit to 17th edition. circuits RCD A 1. 32amp upstairs sockets (original) 2. 32 amp cooker socket...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock