Hi. Penny for a thought anyone. I'm still in holiday mode from yesterday...

Just been to a house after a plumber refused to touch the boiler (not before getting his £200 call out charge) saying there was an electrical fault and showing the customer his voltage pen light up on the water pipes & attic wooden joists saying there "was 20v" through them. The customer asked me to check it over before getting a plumber back.

Indeed on checking my 5V+ pen lit up on both pipes & joists and my voltage tester displayed voltage but of a negligable amount <12v.

The boiler is situated in a seperate part of the house with both water pipes and cables running through a narrow passage above a room joining the two main parts the house.
-TNCS system
- The voltage lowered on isolating the sockets & disapeared totally on isolating the lights. The cabling is messy and could be wrapped around the pipes in places (can't access to see full run).
My first suspicion was induced voltage from the close proximitary of the pipes and cables but that didn't ring right with the joists so I did some tests.

- Gas & water bonding is present.
- IR test on sockets >2Mohm
- IR test on lights 0.23 Mohm

The last time I came across continuity through walls it was a hidden nail in a skirting board catching the r1 to a socket so with the lights failing the IR test I'm thinking a nail etc could be the cause, but, When I reenergised the system less this failed lighting circuit I still have some voltage on the joists / pipes.
Now I'm thinking maybe it's both - induced voltage & a "nail"?
I've got to return to try and locate the light failings but wondered if anyone had any thoughts on the pipes/joists issue?
 
As much as we electricians would prefer to have no currents flowing in the earthing system, that is seldom reality ! Not many electrical systems are perfect, so small currents in the earthing system are not unusual. Fixing such systems can be a big job. so to a large degree it is tolerated.usually small currents are not fatal, but a small tingle does seem to bother some people.
 
why don't you pm PEG he is nearest to you .a couple of beer tokens & a bargain bucket.

A noble and generous suggestion :) - but unlikely...

1) I haven't touched alcohol since i was 15 :eek:

2) He is at a paying gig,and if his customer asked who and what i was,the lie i would have to tell,would be my first :rolleyes:

3) I couldn't start my old Patrol,until the OP had inserted the word "approved",in front of his second test instrument description ;)
 
Hi - Voltpen not helpful here I'm afraid. As mentioned above, I'd use wander to confirm boiler and all those pipes effectively bonded. I suspect a/several circuits have floating CPC as well as IR problems you've already found.
 
To help, please could you describe how you measured the potential difference with your approved voltage tester? Between which two points does the potential difference exist?

What other pds have you measured in this house? eg: MET-N, MET-Water Intake, MET-gas, Boiler casing-MET? Boiler cpc at FCU - pipework.
 
I trust the OP will be giving us an update,or folk are going to start the big supposition stampede...like a practical joking child,with two fluffy angora guinea pigs,in wheel,powering a van de graff generator...

See what i mean...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
manchester

Thread Information

Title
Water pipes & wooden structure showing voltage
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
captaincaveman,
Last reply from
LeeH,
Replies
25
Views
5,494

Advert

Back
Top