What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth?

If all other tests are ok, what are the dangers of the above?

My thoughts are it may indicate a breakdown of the insulation somewhere. However, what are the dangers of this breakdown between neutral and earth? They are both at the same potential already.

What are the other dangers? Is there a risk of fire somehow with poor N-E readings? I can't see how (if all other tests are ok). Although, perhaps the poor IR results are due to a poor connection which is heating up the cable, causing the insulation to breakdown.... so perhaps fire is a possibility?
 
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth?

If all other tests are ok, what are the dangers of the above?

My thoughts are it may indicate a breakdown of the insulation somewhere. However, what are the dangers of this breakdown between neutral and earth? They are both at the same potential already.

What are the other dangers? Is there a risk of fire somehow with poor N-E readings? I can't see how (if all other tests are ok). Although, perhaps the poor IR results are due to a poor connection which is heating up the cable, causing the insulation to breakdown.... so perhaps fire is a possibility?
Had a situation where neutral had failed at meter position so current was tracking back thro cpc because of low ir between n and e.Could have caused a fire.
S
 
Had a situation where neutral had failed at meter position so current was tracking back thro cpc because of low ir between n and e.Could have caused a fire.
S
I can see (with your example), how that could potentially cause an electric shock, but not a fire?
 
As above. The danger is a failed neutral, then the cpc starts carrying the current, and, if the cpc is open somewhere, parts of the circuit and connected equipment that should be at earth potential may be raised to a dangerous voltage.
The other 'danger' is now that most circuits are RCD protected, a N-E leak will cause nuisance tripping.
So apart from nuisance tripping, you would have to have 3 things for 'danger to be present'?

1. Poor IR results
2. Broken neutral.
3. Open CPC.
 
I attended a call-out a number of years ago where the neutral meter tail was broken somewhere and the entire return current for the installation was going back through a neutral/Earth fault on a lighting circuit. The cable sheath was literally bubbling from the heat generated. It's a very real fire risk.
 
The risks arising directly from low (E.g. 0.1-1MΩ) insulation N-E are low to nil. The importance of such a reading, as hinted at above but not explicitly stated, is that it indicates that the wiring is damaged in some way and other hazards might exist that need to be investigated, more serious than the low IR itself. For example, a rodent might have stripped both the line and neutral to bare copper but at the present time only the neutral is in contact with masonry. In which case the low reading alerts and leads you to an unspecified problem, which when investigated, turns out to be high risk.

As mentioned above, hard N-E shorts are different and can cause other more serious problems quite apart from inevitable RCD tripping. With the general use of single-pole OCPD, neutral conductors are not generally protected against overcurrent other than as part of their circuit paired with a line conductor of identical rating. As soon as a main neutral connection or device (e.g. main switch N pole) other than a PEN goes open-circuit, small neutral conductors anywhere in the installation can be seriously overloaded if faulted to earth.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What are the dangers of poor insulation resistance results between neutral and earth?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Lucien Nunes,
Replies
8
Views
7,797

Advert

Back
Top