Discuss What S.I. under risk assessement for omission of RCD in regs in the UK Electrical Forum area at ElectriciansForums.net
T
The Ghost
Ok so as I am moving VERY soon I have packed and sealed all my electrical books away. I don't have access to regs consequently. I am racking my brains regards risk assessment for omission of RCD on sockets. If you read the fine print it references a statutory instrument regards the standard this risk assessment must be made to. In my memory it is S.I. 19 HSA available at the HSE site. Can anyone have a look under 433(I think) and tell me what that S.I. is? I need to advise a customer and better get it right.
Hi - in the 17th Reg 411.3.3 refers. It's Note 3 takes us to App2 item 10 for risk assessment. Not sure if this is it so hit me again if needed.
It is Reg 411.
17th references ‘SI 1999 No 3242’
18th has removed this reference and instead says risk assessment should involve electrically skilled person.
I am interested Vorts why the omission, new install or something with an existing circuit.
I've recently had a customer and a designer refuse to give me a copy of their risk assessment for omission of RCDs, they expected me to put my name to it.
My comment of 'jog on' in slightly stronger language and my directors pulling the project had the desired impact.
I am/have put a cable in for a comms room on the third floor of a commercial building in a locked cupboard accessible by only competent persons (hrmm. so say!) Anyway I have dropped out of the work because of moving so it's a handover and just advising client I have arranged an RCBO from the LL supply and there is a spare MCB as well. Just a courtesy really for the next guy who finishes it. And thought to advise the client regards RA in leaving out an RCD in this instance. All communications and internet will go through this comms room so it is mission critical and moot as to additional protection. Personally I would put it on an MCB. What say you?
It is not likely to be used for general use whilst it is a comms room so I would omit.
And it certainly wont be used for equipment outside on the second (correction!) floor. Also it will be a commando socket so even less likely to be used by the cleaner who broke into the comms cupboard.
16a MCB on radial 4mm T&E all calculated for vd etc. Equipment assessed going on the circuit and manufacturers info taken into account.
I think there was some genuine misreading of the opening post so some later posts have been deleted. I think this has been resolved so can we refrain from unnecessary posts between each other.
Reply to What S.I. under risk assessement for omission of RCD in regs in the UK Electrical Forum area at ElectriciansForums.net
i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Hi All I’m after some advice, I am doing a restaurant fit out involving a number tables that have hot pots built into the table, for customers to...
Hello All. I am taking my 2396 written exam in December this year, therefore i am knee deep in practice papers. In case anyone else is in the...