Filling out the schedule of circuits when using a Split DB 5/5.
The main switch details are noted in Part 8.
Do you the enter the Rcd details in the schedule Part 11,then enter the corresponding circuit details.
Also being mcbs what do enter in the column for Rcd operating box, i usually put N/A..even though they are Rcd protected but are mcbs.
 
Been discussed before.
This is how I do it.
I know some will disagree about filling in the RCD rating on each circuit below the RCDs. I just feel that it's helpful to see at a glance whether a circuit is RCD protected or not.

Edited to add that I now fill in the RCD type (AC ,A, B etc). In this older cert I just had it as N/A.
Screenshot_20210328-150745_OneDrive.jpg
 
Ok... may now do this too..not spoken with the Niceic about this yet..it’s one of those,a simple question but no definite right or wrong.
 
Been discussed before.
This is how I do it.
I know some will disagree about filling in the RCD rating on each circuit below the RCDs. I just feel that it's helpful to see at a glance whether a circuit is RCD protected or not.

Edited to add that I now fill in the RCD type (AC ,A, B etc). In this older cert I just had it as N/A.
View attachment 83913
The garage has a ring with 1 socket on it? Major overkill
 
Been discussed before.
This is how I do it.
I know some will disagree about filling in the RCD rating on each circuit below the RCDs. I just feel that it's helpful to see at a glance whether a circuit is RCD protected or not.

Edited to add that I now fill in the RCD type (AC ,A, B etc). In this older cert I just had it as N/A.
View attachment 83913
all cables in conduit? ref. method B?
 
not spoken with the Niceic about this yet.
Our NIC inspector did speak to us about it and the advice was if the RCD is for additional protection ... record the highest 5x measurement. If the RCD is for fault protection ... record the 1x measurement but that applies to the RCD not any MCB's which I personally do not show a RCD time for.
 
Our NIC inspector did speak to us about it and the advice was if the RCD is for additional protection ... record the highest 5x measurement. If the RCD is for fault protection ... record the 1x measurement but that applies to the RCD not any MCB's which I personally do not show a RCD time for.
Fine. But what if the RCD protects some circuits that don't require additional protection?
 
Well it shows that it’s difficult to fill out these forms,& mistakes are made..I always forget something when completing even missed out the tester information required.
 
Well it shows that it’s difficult to fill out these forms,& mistakes are made..I always forget something when completing even missed out the tester information required.
The biggest problem with all these forms is that they hardly ever get reviewed and proof read properly once they are filled in, that is until the client posts it on here
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
What’s your take on this
Prefix
NICEIC Certification Scheme 
Forum
Certification NICEIC, NAPIT, Stroma, BECSA Forum
Start date
Last reply date
Replies
14

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
cliffed,
Last reply from
UNG,
Replies
14
Views
6,075

Advert

Back
Top