This is my first post so lets see how it goes.
Can anyone advise me on the following installation.
Have been asked to install wiring to a garden hot tub (24A max demand).
Its nearly 70m from the house and the customer also requires fan heater in the shed and some lights. Max demand in total about 38A. Cable calcs have given 10mm cable as voltage drop is getting close to 5% max.
I intend to fit a Henley block on the incoming tails to a new C.U.
This will have a 40/50A, 100mA RCD and a 50A Type C MCB.
In order to meet disconnection time I need to install an earth rod and make the new install a TT system.
Thats ok but should I use 2 core SWA, bond the steel armour the the house earth and use the TT system for the protection for the rest?
Was going to fit a 40A 30mA RCD with 32A, 16A and 6A MCB's in a CU in the shed.
Comments would be appreciated.