Hi, looking for some advice,
6mm swa allready installed to a hot tub
Client now wants additions and my calcs say the original swa is allready too small.
26a but its120m run, im advising 16mm 2core.

However the swa installed is 4 core so was thinking of doubling cores together to save on time/ costs and putting rod in.

Any thoughts or potential issues with this?
 

Multicore 90°C Armoured Thermosetting Insulated Cables​

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage:230V

Load:5.98kW / 26A

Length:120m

Method of Installation:Direct in ground or in ducting in ground

Cable Size:16mm²
 
My calculations also indicate 16 mm² for the hot tub alone. Doubling up using the other 2 cores of the 4 core would result in the equivalent of 12mm² at best.
A new cable run is the only option I can see.
 
Feel bit sorry for bloke and doubt he will pay for upgrade, and im not planning on doing works.
Was just thinking if in theory by doubling the existing cores would improve the current installation.
 
My calculations also indicate 16 mm² for the hot tub alone. Doubling up using the other 2 cores of the 4 core would result in the equivalent of 12mm² at best.
A new cable run is the only option I can see.

Odd, I get 10mm for the hot tub.

What voltage are you basing your calculation on? The load is stated as 6.5kW 26A which only makes sense if that rating is at 250V.
Based on 250V I get 10mm

But if you adjust the load for a 230V supply (assuming the majority of that load is heating and so resistive) it will be running at 5.5kW and 24A and again I get 10mm as being suitable.
 
Feel bit sorry for bloke and doubt he will pay for upgrade, and im not planning on doing works.
Was just thinking if in theory by doubling the existing cores would improve the current installation.

Yes doubling up the 4 core will improve the situation, it may not make it perfect but it will improve it.

But does the hot-tub work currently? If it does then it suggests that the volt drop is not currently so excessive that it will cause a functional issue.
Does the hot tub have a minimum supply voltage rating? (rememeber the percentages given in the regs are intended for use when the voltage tolerance of a load is unknown, not necessarily a hard limit for every circuit)

Obviously the fact that something works in its current states doesn't guarantee safety, but it does indicate that the supply may be functionally adequate.

Have you measured the voltage drop on the hot tub circuit?
 
Odd, I get 10mm for the hot tub.

What voltage are you basing your calculation on? The load is stated as 6.5kW 26A which only makes sense if that rating is at 250V.
Based on 250V I get 10mm

But if you adjust the load for a 230V supply (assuming the majority of that load is heating and so resistive) it will be running at 5.5kW and 24A and again I get 10mm as being suitable.
Let me do it again. I think I may have used 32 amps as the load...

Edit:
Recalculated using 26 amps, still get 16mm² due to volt drop.

Edit 2:
I used installation method D1 assuming an underground cable run.
 
Last edited:

Ah, that'll be the difference.

We have been given a load of 6.5kW and 26A which only makes sense if that is at a rated voltage of 250V.

So you either need to calculate at the rated voltage or adjust the load value for the voltage you are going to do the calculation at.
Adjusting the load for a voltage of 230V (assuming the load is resistive, or mostly resistive, heaters) it becomes 5.5kW and 24A at 230V.
 
Ah, that'll be the difference.

We have been given a load of 6.5kW and 26A which only makes sense if that is at a rated voltage of 250V.

So you either need to calculate at the rated voltage or adjust the load value for the voltage you are going to do the calculation at.
Adjusting the load for a voltage of 230V (assuming the load is resistive, or mostly resistive, heaters) it becomes 5.5kW and 24A at 230V.
Thanks for pointing this out, however I believe I fully understand the nature of resistive loads in this context.

However, whichever way I calculate it, even with a design current as low as 24 amps, it doesn't reduce the volt drop enough for a 10mm² cable to comply with maximum 5% volt drop.

I just noticed the OP has given new figures from the rating plate of 220 V, 29 amps.
Using these figures, volt drop is still the limiting factor, according to my reckoning.
 

Reply to Swa install to hot tub in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
436
There’s is currently a 3 core 6mm swa installed/40amp breaker, the garden room has its own consumer unit with a 32amp ring circuit and 6amp...
Replies
8
Views
3K
Just pricing up a job for a back garden hot tub (32A fixed supply, not the 13A temp type). 6mm SWA to rotary isolator etc. all fine but I'm...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock