Hi. could a Zs test be done at an isolator terminals instead of at the end of a circuit or equipment in any circumstances? I'm sure that i read this was OK but was always taught it was at the end of the circuit.
It can be done anywhere on the circuit but it's pointless unless it's done at the last connection. Why where you thinking about doing it at an isolator?
It depends what is after the isolator IMHO. If the isolator is the final connection to a piece of fixed equipment then that is where you would take the Zs reading (if it is the last point on the circuit). If the isolator is inserted within the fixed wiring, e.g. feeding a socket for a built in appliance in a kitchen, then no you can't take the reading at the isolator.
Quote........."The measurement should be made at the point or accessory electrically furthest from the supply of the circuit"
Well tbh Ive been wiring a few Mitsubishi Ecodan Air Source Heat Pumps and always take my Zs reading at the rotary isolator. The cost of the ecodan unit is £4500 and dont really want to damage the unit! Testing Zs at low current also. :)
If that is the end of the primary fixed circuit, that is where you would make the Zs test from. I'm taking it, that the isolators you refer too, is adjacent or fixed to the equipment it is supplying??
:banghead: I find these college lecturers really annoying these days, Calculated ZS tests, why? Bloody trade is going backwards IMO
This is what they are being taught now on the course mate, I had a Electrical Trainee with me for a week's experience while I was on a 3 phase install small industrial unit, we did the install then obviously started testing, he tested while I stood at his side and was gobsmacked when the only test he didn't do was a zs when I asked why he felt it was ok to leave it it out is answer was the guy who ran the course said as long as you get your R1 + R2 then there is no need for zs and they only charged him 2500.00 for that little lesson. When I tried to explain it was probably the easiest test in the sequence to do he just gave me a blank expression. The times they are a changing my friend.
Your right they are changing, we had a good debate about this very topic a while back regarding verification and Sintra came up with a valid reason which should be told to these college lecturer's, I can't find the thread at the moment but will do I'm sure and I may even post a link to it in my sig so these college lads can see real reasons for testing rather than calculation, as you rightly pointed out it is a very simple test to carry out, it amazes me that trainees are taught to calculate and avoid this test.
I would be interested in seeing that debate if you can resurrect it mate. My biggest gripe is with the muppets teaching these courses, they can't have any hands on experience to be offering some of the advice that they do! . But the biggest concern for me is to the pupils on these courses, because like my example above if had not sat the lad down and gave him some valid reasons , then I know for a fact he would have gone away still thinking that it is ok to omit a very important part of the test sequence. I will be back on later as I'm off to earn a few bob now so hopefully you will be able to find the debate you mentioned.
I think the reason was that testing Zs would highlight a high resistance through an MCB etc, which a calculation obviously would not. IMO whats the point in owning a multifunction tester and then calculating results!
No harm in being taught how to calculate Zs etc, but testing is the only way to be sure that a circuit is complying in the field!!
Having said that what do you guy's really expect from someone that has been through a 17 day/5 week course at a training centre??
Tbh there is no harm in calculating the Zs. When testing a circuit that is rcd protected and has sensitive equiment attached. Testing on low current no trip will give you a false reading.
You guys love to put everyone down.. Must make you feel good?
And i have not done a 17 day/5 week course at a training centre....
I done my 2330 level3
I don't think the last few comments were aimed at you personally.
As Tel Mentioned you were not the Target
It is these modern college lecturers who have brain washed the trainees today to calculate. Ridiculous, one of the easiest tests carried out and they are promoting calculation haha.
If you state "tested to isolator" on the cert i dont see a problem with it.. Aslong as person ordering the work is aware. You would insulation resistance test to the isolator also! This said i would also Zs at futhest point in circuit!
The isolator would in the majority of cases, be the furthest point on the ''Fixed'' installation. You wouldn't normally test IR or Zs past that point.
Is it something to do with this Live testing counts as Live working bullshyte?!?!
Who are these people?
it it does make sense for them to teach how to calculate Zs as like already stated it is classed as live working. Elf and safety gone mad again ? Well probably not when you think some of the trainees have very little electrical knowledge and even less practical experience. Some Should not be let loose with anything more than a 9V battery.
Why on earth would it or can damage your unit ?
Your not getting confused with testing Zs and mistaking it with 500vdc IR are you ?
Not trying to be condersending buddy but Zs at the extremely is not connected to your unit.