I hope your not using the steel braid as your CPC intp the equipment??
Nope im not using the steel as a CPC...
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs test with isolator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I hope your not using the steel braid as your CPC intp the equipment??
Tbh there is no harm in calculating the Zs. When testing a circuit that is rcd protected and has sensitive equiment attached. Testing on low current no trip will give you a false reading.
You guys love to put everyone down.. Must make you feel good?
And i have not done a 17 day/5 week course at a training centre....
I done my 2330 level3
Thanks
Sorry to jump the gun!
But in all honesty there is no problem with calculating the Zs. :xmas:
Is it something to do with this Live testing counts as Live working bullshyte?!?!
Who are these people?
Why on earth would it or can damage your unit ?Well tbh Ive been wiring a few Mitsubishi Ecodan Air Source Heat Pumps and always take my Zs reading at the rotary isolator. The cost of the ecodan unit is £4500 and dont really want to damage the unit! Testing Zs at low current also.