Currently reading:
undersized SWA to garage code?
Discuss undersized SWA to garage code? in the UK Electrical Forum area at ElectriciansForums.net
Hi,
Got an undersized cable going to a garage not sure how to code it:
Cable is 2 core 2.5 SWA at least 40m long
Cable comes of a 15a 3036 fuse in the house and splits into DB3 (a 20a switch fuse coming of the live side of DB4 main switch) and DB4 an old wylex rcb main switch board with 2 16a and 1 6a plug in RCD.
Obviously voltage drop way above 5% but essentially the whole lot is protected by a 15a fuse in the house so more a nuisance than dangerous.
The earth is exported via the steel sheaf from the TN-S in the house. I know it's generally advised that anything over a 20m run should be spiked but I need a reg to back that up.
Any thoughts?
Steve
I'll go along with post 2. Where did you hear the 20m rule?
The guy may come from an industrial background. Most specs and designs for large areas have a 20-30metre rule of thumb, to keep lengths of final circuits down to manageable length. Depending on circuit, I would always try and design final circuits under 30mts, by trying to fit sub boards.
Sometimes you can't such as hi bay lighting, or areas where siting another board is just not possible, other than in the electrical/technical room.
But the OP is a distribution circuit and so I would not thought any rule on distance would apply as such
Thanks for the responses.
Goes like this:
Origin > DB1
Origin > DB2
DB2 15a Fuse (3036) > 2.5 2 core SWA >Garage>DB3 and DB4 (sheaf used as earth)
DB3 is a 20a Switch fuse
DB4 is an old wylex board RCD main switch to 2 x 16a and 1 x 6a plug in MCBs
Also looking for R1 + R2 tables using the steel sheaf as a CPC..
Cable to garage voltage drop safe to declare an exception?
Hi,
I've got a customer with a 2.5mm 2 core swa cable on a 15a 3036 fuse feeding a garage 40m away
Although the cable can easily handle the current it's more than 5% voltage drop.
The earth is via the armour.
I've recommended a board change for other reasons but i've suggested a 3core 6mm swa of a 20a mcb feeding a garage box with a 6a and 16a for lights and some sockets. 6mm gives me a big enough CPC.
He's not keen.
Given that we're talking about a voltage drop which won't make much difference to what he'll be using (lights, a drill etc) the only safety problem I can see is the size of the cpc (armour). Does he have the option of me installing an earth rod to get over the cpc size and then signing of the cable size on the cert as an exception? Not ideal but basically safe?
Its a TN-S BTW
Thoughts ?
Re: Cable to garage voltage drop safe to declare an exception?
Hi Steve,
What's the design cuttent of the garage circuit? From what you say , lights and a drill, it won't be much. I would of thought the vd would be fine.
The armour for cpc should be ok too, I'm assuming no extraneous conductive parts.
Garage has a 20a switch fuse and a board with 2 x 16a and 1 x 6a mcb. So loads are more likely to pop the house fuse.
So I guess the voltage drop isnt really a safety issues so a C3.
Just need to get a value for the armour as a cpc. Guess I'l just measure it!!
Cheers
s
Cheers
s
or measure the loop impedance art a garage socket.
There's a lot more to correct cable sizing than just reading the tabulated ccc.
Agreed, so I did a quick calc! Based on a 15A load ( fuse rating at origin ), multi core 2.5mm swa, buried, 40m, ze 0.8ohms (TN-S), 5% VD. These are all assumed at worst case!
Correction factors:
Ci : 1
Cg : 1
Cc : 0.9
Ca : 1
Cf : 0.725
Total correction : 0.653
Adjusted cable rating : 22.97A
Calculated R1 + R2 : 0.71 ohms ( based on a core rather than armour ). Will be lower when calculated with armour.
Calculated Zdb : 1.51 ohms
Max Zdb at 0.4s : 2.43 ohms
VD : 4.696%
All still seems ok!
Thanks for this TD , very useful.
Problems:
You say that:
<Resistance> Will be lower when calculated with armour.
But according to this manufacturers tables the resistance of the armour (8.8 ohms/km) is a higher than the 2.5 copper(7.41ohms/km). how does this affect your calcs?
Exported earth TN-S:
The armour is too small to for the earthing requirements at the garage end?
Any thoughts
many thanks for this.
Regads
Steve
best regards
Steve
Appendix 4 - Cable Data-Resistance, Impedance and []R1 + R2? Values - Guide to the Wiring Regulations - Locke - Wiley Online Library
To all contributors
I started another thread on this subject in General to discuss remedial works. Unfortunately it has been frozen. many thanks to the people who posted replies to that thread and my apologies for not replying. Apologies if this drifts into solutions as was intended in the new thread.
Regards
Steve
Problems:
You say that:
Any thoughts
Regads
Steve
best regards
Steve
Hi Steve
The actual CSA of the steel for 2.5mm SWA is 17mm, minimum CSA required as per table 54.7 is 5.7mm.
It's more for disconnection times really! The max zs at 80% for a bs3036 is 1.944ohms. Your actual is more on the lines of 1.603 (best to test Zdb at the garage).
Cheers
Cheers
Many thanks TD. I didnt realise that it doesnt matter if its steel or copper. I thought the CSA was a representation of the resistance/km.. If it is then obviously the material is relevant.
I'm installing a new CU. I'm thinking of putting the garage on a timed RCD in the house to a garage box with a std RCD a 6a and 16a MCB.
Thanks again.
S
Thanks again.
S
a what?
Thanks again.
S
It does matter what material it is made of, and you use the relevant K factors to calculate for different materials.
Why does it need a time delayed RCD?
Reply to undersized SWA to garage code? in the UK Electrical Forum area at ElectriciansForums.net