It is as the name surgests a report on the condition fully or in part of the electrical installation at that time and can be used to see if the installation has deteriated since the last .
 
Replies to date just go to show how this is interpreted. GN3 guide for me.

But I suspect that a considerable amount of testers don't do full dead tests as part of the eicr.

GN3 specifically states that, on an EICR, a Zs test can be used instead of R1+R2 to prove that the earth fault path is OK.
 
That is for testing a new install covered under 2394 not 2395 which is periodic there are diferent requierments, it is down to the tester what test needs to be carried out and agreed with the customer and clearly stated on the cert
Just trying to show the OP the correct procedure for testing RFC
 
For all those saying a Zs can be used to prove an earth fault path exists, fair enough. However, there's more issues at play with a RFC as I've been taught. The three I can think of are:
  • Must be a complete ring
  • Must have no interconnections (so no rings within rings)
  • Must have no daisy chains of spurs without additional protection
So, Zs proves earth continuity. However, it doesn't prove any of the above. Only the 3-stage RFC testing procedure can, hence why we do it in the first place. An EICR is carried out to prove how safe the installation is, but what would you code each of the three items above if there were issues - I'd reckon a C2 in each case? So there exists some unique situations for RFCs that can be dangerous, and we're not going to test for them at an EICR? If that's the case, why bother testing for them at installation either?

Anyway, to answer the OP - full RFC testing procedure for me every time. Okay, that means disconnecting a few cables at the board (minimal dismantling, I get that) but the pros of a full test far outweigh the cons of disconnecting a few cables momentarily.

You'll commonly hear it said, the less writing an EICR has on it (as in test results, limitations etc), the less that bit of paperwork is worth.
 
You should at least do an end to end test and a figure of eight, this should give a rough indication of the Zs.
 
Spoke to the nic he said no two places are the same it's about your feel on the installation if you find there as been alteration then do it if you feel it looks good readings good end to end then it's ok all bout your professional judgement I think I'll carry on doing it the way I have been all test that's involved just bit shocked what some colleges are teaching
 
Spoke to the nic he said no two places are the same it's about your feel on the installation if you find there as been alteration then do it if you feel it looks good readings good end to end then it's ok all bout your professional judgement I think I'll carry on doing it the way I have been all test that's involved just bit shocked what some colleges are teaching
That fence they sit on must be well worn.
 
However, it doesn't prove any of the above. Only the 3-stage RFC testing procedure can, hence why we do it in the first place.
Again I would point you to the guidance in Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made. Again, like I said, end-to-end tests on the circuit conductors would seem to be reasonable in these circumstances. Obviously the Zs of all socket outlets should also be verified.
 

Reply to eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock