Exterior socket on PME system

Discuss Exterior socket on PME system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
I'm installing a 32A socket on a PME system.

The socket itself is indoors and is on its own RCBO.

The intention is to use the socket for power for outdoor events.

My technical help line says that I should disconnect the earth at the socket then TT it. It seems to me that that would make it more dangerous.
 
Speaking to them again , they also talked about 711. However they're now suggesting that a risk assessment with a warning that only CLass 2 equipment should be used and a non standard socket fixed.

How likely is it that the supply neutral would ever be lost?
 
Sounds like they are back tracking. One way you could look at it is you have been asked to install a socket, by good chance internally. Do this because how they choose to use the power from the socket is up to them. Some people lose hours of sleep worrying about lost neutrals, I do not however it is something that occurs.
 
Personally I would just fit one and have done.

However you could please everyone by installing a decent rod with a good Ra and connect it to the MET of the house.
It would have to be a very good Ra. :)

If max demand (for the installation, not just the outside socket) is, say, 30A, then you need an Ra less than 3.35Ω if you want a touch voltage less than 70V (using the formula in A722.3 for EV charging in single phase installations, which is just the potential divider formula rejigged).
 
Speaking to them again , they also talked about 711. However they're now suggesting that a risk assessment with a warning that only CLass 2 equipment should be used and a non standard socket fixed.

How likely is it that the supply neutral would ever be lost?

Regarding the first suggestions (Class 2 only), this is a complete non-starter, unless there's a specifc item of equipment to be used. For general PA... no chance.

Regarding the second question: there was a study done, "Charging of Electric Vehicles at Domestic Dwellings Using Protective Multiple Earthing (PME) - Risk Analysis PE01417/2012/1" (Commentary on the Wiring Regs mentions it). Increase in individual risk (seriously injured or killed) was 1.1x10^{-6} to 7.8x10^{-9} (sorry, not sure how to get superscript!) - worst case just more than 1 in a million. That's only for people in contact with EV charging systems (not the whole population). Even with risks that low, extra measures are recommended to reduce the risk "if reasonably practicable to do so" such as putting in an earth rod with low Ra.

In the DPC of the 18th Edition, they are proposing to remove the "if reasonably practicable" option in 722.411.4.1.
 
It would have to be a very good Ra. :)

If max demand (for the installation, not just the outside socket) is, say, 30A, then you need an Ra less than 3.35Ω if you want a touch voltage less than 70V (using the formula in A722.3 for EV charging in single phase installations, which is just the potential divider formula rejigged).

It's RCD protected...

It's solving the problem of a lost neutral on the DNO side.

Even then an Ra of 3.35 isn't a huge effort.
 
It's RCD protected...

It's solving the problem of a lost neutral on the DNO side.

Even then an Ra of 3.35 isn't a huge effort.

I'm confused. Surely an RCD won't help for additional (shock) protection when there's a missing PEN (on the DNO side)? Current flows out through the L, through the RCD, through the load, back through the N, same current back through the RCD (so, balanced), to the PME block (where earthing conductor is connected to PEN), to MET and through CPC to exposed conductive parts, through body of person, to earth.

I agree that having an earth electrode with good Ra is better than not having one (for PME) to reduce the touch voltage in the event of loss of PEN on the supply side. To remove the shock risk requires a very low Ra, and something like 3.35Ω, depending on the local ground conditions, may be... challenging. :)
 
Draw it out Steve, the N>E link is before the RCD, so current flowing down the PE will not go through the RCD causing an imbalance.
 
On quickly reading and passing through, I've got to agree with happy steve.

Scenario: Class 1 appliance, no faults present anywhere on installation except broken neutral on PEN conductor. Current is balanced through RCD, earthed conductors rise to a dangerous voltage, link between Class 1 appliance and earth made via a person, RCD is going to say "hey, this looks alright to me"

What am I missing?
 
Last edited by a moderator:
Don't know, my understanding, limited as it is, is broken PEN conductor, is your worst case scenario (don't have nightmares folks) RCD or no RCD.
 

Reply to Exterior socket on PME system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top