Discuss Exterior socket on PME system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I'm installing a 32A socket on a PME system.
The socket itself is indoors and is on its own RCBO.
The intention is to use the socket for power for outdoor events.
My technical help line says that I should disconnect the earth at the socket then TT it. It seems to me that that would make it more dangerous.
Speaking to them again , they also talked about 711. However they're now suggesting that a risk assessment with a warning that only CLass 2 equipment should be used and a non standard socket fixed.
How likely is it that the supply neutral would ever be lost?
Sounds like they are back tracking. One way you could look at it is you have been asked to install a socket, by good chance internally. Do this because how they choose to use the power from the socket is up to them. Some people lose hours of sleep worrying about lost neutrals, I do not however it is something that occurs.
Personally I would just fit one and have done.
However you could please everyone by installing a decent rod with a good Ra and connect it to the MET of the house.
It would have to be a very good Ra. :)
If max demand (for the installation, not just the outside socket) is, say, 30A, then you need an Ra less than 3.35Ω if you want a touch voltage less than 70V (using the formula in A722.3 for EV charging in single phase installations, which is just the potential divider formula rejigged).
Regarding the first suggestions (Class 2 only), this is a complete non-starter, unless there's a specifc item of equipment to be used. For general PA... no chance.
Regarding the second question: there was a study done, "Charging of Electric Vehicles at Domestic Dwellings Using Protective Multiple Earthing (PME) - Risk Analysis PE01417/2012/1" (Commentary on the Wiring Regs mentions it). Increase in individual risk (seriously injured or killed) was 1.1x10^{-6} to 7.8x10^{-9} (sorry, not sure how to get superscript!) - worst case just more than 1 in a million. That's only for people in contact with EV charging systems (not the whole population). Even with risks that low, extra measures are recommended to reduce the risk "if reasonably practicable to do so" such as putting in an earth rod with low Ra.
In the DPC of the 18th Edition, they are proposing to remove the "if reasonably practicable" option in 722.411.4.1.
It's RCD protected...
It's solving the problem of a lost neutral on the DNO side.
Even then an Ra of 3.35 isn't a huge effort.
I'm confused. Surely an RCD won't help for additional (shock) protection when there's a missing PEN (on the DNO side)? Current flows out through the L, through the RCD, through the load, back through the N, same current back through the RCD (so, balanced), to the PME block (where earthing conductor is connected to PEN), to MET and through CPC to exposed conductive parts, through body of person, to earth.
I agree that having an earth electrode with good Ra is better than not having one (for PME) to reduce the touch voltage in the event of loss of PEN on the supply side. To remove the shock risk requires a very low Ra, and something like 3.35Ω, depending on the local ground conditions, may be... challenging. :)
Draw it out Steve, the N>E link is before the RCD, so current flowing down the PE will not go through the RCD causing an imbalance.
On quickly reading and passing through, I've got to agree with happy steve.
Scenario: Class 1 appliance, no faults present anywhere on installation except broken neutral on PEN conductor. Current is balanced through RCD, earthed conductors rise to a dangerous voltage, link between Class 1 appliance and earth made via a person, RCD is going to say "hey, this looks alright to me"
What am I missing?
Don't know, my understanding, limited as it is, is broken PEN conductor, is your worst case scenario (don't have nightmares folks) RCD or no RCD.
Okey dokey :) The squiggles inside the circle are meant to represent an RCD. In the event of a broken PEN (and no other fault), the same current passes through both poles of the RCD and there is no imbalance. The current then flows through the CPC, through the person, and to earth.
The picture below just shows that the formula A722.3 is correct.
So I still maintain that an RCD will not help in this situation.
Ok long day so bear with me. Informative video but it seems to me that it only applies if there is no other path to earth than the affected person.
If the PEN is broken then would the current not flow back through the bonding to true earth especially if I introduce earth rods into the system?
Could I introduce an earth rod connected to the earth terminal in the socket?
Sorry South Spark for meandering off a bit...
Re your first question... yes it would. There has been some to-ing and fro-ing about the numbers, but essentially yes, having an earth rod would make the situation safer.
Re your second question... If you mean, "connect the earth rod to the socket and still retain the CPC from the TN-C-S" I would advise against this, unless you have 10mm earthing conductor all the way back to the MET (for the same reason that bonding needs to be 10mm). If you mean, "Run the CPC to the socket but don't connect it to the earth pin (or anything exposed) and connect the earth pin to a local rod," then this sounds like "TT-ing your shed" without a sub-board. The protective device (and additional protection) would be on one earthing system, and the socket-outlet on another. I don't know if this is relevant or not, and I've reached the limit of my knowledge about whether this would be permitted or advisable.
I suppose the way of complying to keep everyone (incluing your CPS advisors) happy would be to treat this 32A socket as a separate board and TT it. So install an RCD garage subboard with the socket nearby, put this sub-board on the earth rod, and follow the usual procedure for making sure exposed conductive parts from the two different earthing systems are not simultaneously accessible (411.3.1.1).
If it is to be used for outdoor events then you'd do well to read up on the requirements of BS7909 'code of practice for temporary electrical systems for entertainment and related purposes'
This is becoming more commonly recognised in the industry, and councils are increasingly requiring compliance as part of event licensing.
As it stands you may find you have a grumpy customer on the phone when the event electrician comes along and refuses to use the socket as it is non-compliant.
Just checking, that you agree an RCD will not afford additional protection, in the case of a broken PEN conduct?
.... in the case of a broken PEN conduct?
Is there a way forward with this situation .
Detecting under voltage at the supplied load ,
Supply voltage being shared between Load, and unfortunate Human earth connection .
(remebering some old RCD technology ran warm
and needed a suppy to stay latched ON )
Reply to Exterior socket on PME system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...