Why have you energised a circuit with no cpc's connected?
how discovered
the earth was not in play when doing a r1+r2 to see if I had the wright circuit by leaving off the earths when putting the socket and see tester in to indicate that a had that circuit .and then it showed me earths present when the cpc earths not connected .
 
I still don't see what you are hoping to find or achieve here. It could be supplementary bonding, it could be metal dual boxes. It's a parallel path somewhere. If I was the customer I wouldn't like to be paying for all this unneeded work.
 
I am now checking for any parrell paths so here it goes up stairs ring cpc r1. In board in r2 wander lead mothod testing to boiler 23.6 ohms and all pipe work the same . water service disconnected and gas .any thouhts
 
sorry if I repeat anything said/done.....but forget the plug in tester. Use your multimeter on all RFC's dead test end to end & also test for any cross over of RFC's r2 on cct1 to r2 cct2 (neutrals as well)etc and RFC r2 to the met with other ccts attached...anything ?
If you want to work live test at sockets removing neutral from cct ?
 
If I understand correctly, you have one specific RFC that has a connection to earth somewhere, despite the installation earth & bonding connections all being disconnected?

As others have mentioned, I'm not totally understanding why this is a problem? I'm assuming nothing is tripping, and you just want to know why, rather than needing to disconnect this other earth? Normally I'd just move on.

Assuming you really do need or want to know, then can you not just split the RFC into two, and find which half is still earthed. Then repeat with the earthed bit, until you narrow it down? Just like looking for any other fault on an RFC?

And when you say earthed, are you measuring a resistance to the suppliers' earth? If so, what value (from each end of the RFC)? Or did I recall seeing you are measuring Zs values on this RFC (with main earth and bonding disconnected)?
 
come monday, when buzz has recharged his dilithium crystals, he''ll find it in a nanomonth.
 
Usually it's me trying to find out why something does not compute - go Buzz go !
Perhaps confirm IR on that circuit and then isolate any backbox connections. With 23.6 Ohms it sounds like there's "an earthrod" attached :) .
 

Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top