, and what is the issue here , you have a parallel earth path
the only circuit which was live was up stairs ring no earths connected but showing earths ,considering it a empty house .
All cpc's and earthing has been disconnected from the Consumer Unit, and you have now energised the circuits?
 
Why have you energised a circuit with no cpc's connected?
 
Why have you energised a circuit with no cpc's connected?
how discovered
the earth was not in play when doing a r1+r2 to see if I had the wright circuit by leaving off the earths when putting the socket and see tester in to indicate that a had that circuit .and then it showed me earths present when the cpc earths not connected .
 
If the IR test's are ok why are you bothered? Parallel paths aren't considered a bad thing.
 
If the IR test's are ok why are you bothered? Parallel paths aren't considered a bad thing.
the trouble is am over thinking on this .or just F88k it .
if the earths are not their before putting the cpc in .I would like to know how the hell is the earths coming from .
 
I'm with Sparkdog here
I wouldn't rely on a plug tester for anything.
Perhaps there is supplementary bonding somewhere, it used to be taken off the nearest cpc.
My guess supp bonding under the bathroom floor between earthed copper pipe and your RFC earth.
 
  • Agree
Reactions: 123
I still don't see what you are hoping to find or achieve here. It could be supplementary bonding, it could be metal dual boxes. It's a parallel path somewhere. If I was the customer I wouldn't like to be paying for all this unneeded work.
 
Any sneaky external installs spurred from RFC ?
(CHARLIE DIMMOCK Water feature)
 
  • Funny
  • Like
Reactions: DPG and Rpa07
time to call in the experts.:

 
I am now checking for any parrell paths so here it goes up stairs ring cpc r1. In board in r2 wander lead mothod testing to boiler 23.6 ohms and all pipe work the same . water service disconnected and gas .any thouhts
 
sorry if I repeat anything said/done.....but forget the plug in tester. Use your multimeter on all RFC's dead test end to end & also test for any cross over of RFC's r2 on cct1 to r2 cct2 (neutrals as well)etc and RFC r2 to the met with other ccts attached...anything ?
If you want to work live test at sockets removing neutral from cct ?
 
Are the sockets surface or sunken? If sunk do they have a fly lead to the box and is the wall damp at all?
 
Vort all boxes are sunk in the walls the. Fly leads that are in should not show any earths it should be clear .
 
If I understand correctly, you have one specific RFC that has a connection to earth somewhere, despite the installation earth & bonding connections all being disconnected?

As others have mentioned, I'm not totally understanding why this is a problem? I'm assuming nothing is tripping, and you just want to know why, rather than needing to disconnect this other earth? Normally I'd just move on.

Assuming you really do need or want to know, then can you not just split the RFC into two, and find which half is still earthed. Then repeat with the earthed bit, until you narrow it down? Just like looking for any other fault on an RFC?

And when you say earthed, are you measuring a resistance to the suppliers' earth? If so, what value (from each end of the RFC)? Or did I recall seeing you are measuring Zs values on this RFC (with main earth and bonding disconnected)?
 
come monday, when buzz has recharged his dilithium crystals, he''ll find it in a nanomonth.
 
  • Funny
Reactions: DPG
Usually it's me trying to find out why something does not compute - go Buzz go !
Perhaps confirm IR on that circuit and then isolate any backbox connections. With 23.6 Ohms it sounds like there's "an earthrod" attached :) .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

buzzlightyear

Arms
Supporter
~
Joined
Location
star command
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Heavily Qualified Electrician / Teacher / Tutor - etc

Thread Information

Title
Now i am pulling my hair out
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68

Advert

Thread statistics

Created
buzzlightyear,
Last reply from
buzzlightyear,
Replies
68
Views
6,300

Advert