If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
 
Where was the other lead of the DMM, still the MET? Did you measure the AC voltage? That would cause a symmetrical influence on the resistance readings. I agree though that some electrolytic potential does usually show up that at least makes a difference between the two indications, or even swamps the DMM source making one of them negative.
 
  • Agree
Reactions: static zap
Yes, it was basically the same test points. It was starting to rain so I didn't spend much more time checking AC volts, etc, but as the system is not finished yet there will be a more formal test when its all done.
 
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
10 ohms. That must get you an automatic nomination for "rod of the year award". Well done
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
Absolutely. I have never heard of such a good result. Very encouraging. Yes a great plan B for TN-S. But with those soil conditions another 2 rods could quite possibly get you a plan B for a TNC-S Istallation as well. Wish we had conditions like that over here
 
  • Like
Reactions: pc1966
Wish we had conditions like that over here
Electrically it is way better than I expected. But there is a down-side to the wet clay below the local ground surface: when you get it on your shoes it behaves, in every way but smell, like you have stood in a dog turd!
 
Electrically it is way better than I expected. But there is a down-side to the wet clay below the local ground surface: when you get it on your shoes it behaves, in every way but smell, like you have stood in a dog turd!
Bearing out the old saying "nothing in life is free"
 
I think a reading below 200ohms is good and not unstable this is from the 16th ed
 
  • Disagree
Reactions: davesparks

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Happy earth rod day
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
pc1966,
Last reply from
jay sean,
Replies
8
Views
1,618

Advert