Hi guys, I am adding a lighting circuit to a Ring main 32 A. Can I just use a 6A MCB type B in a box on DIN rail to supply my lighting. I am using 1.5mm cable after the 6 A MCB.
Thanks for your advice!
 
As above, a FCU with a 5A fuse is the simplest option, just added as if it were a socket on the ring.

Or even as a spur. Though personally I dislike spurs due to the options for abuse (adding more later and not limited to 13A) as well as the higher risk of a conductor not being properly clamped if there are 3 (or more!) in an existing socket.
 
My issue is though in terms of short circuit by the lght, both the 6A mcb and the 32A mcb trigger. I would rther the lighting mcb to trigger only. shall I change into a rcbo o a different cb?
 
well , the 6 AMP mcb type B is overload and short circit protecting the lighting circuit. Only issue was to avoiding the 32 AMP ring mcb to trigger, hence the alternative CB . It needs calculating the arc current etc to determine the right mcb, but honestly I cannot bother as long as circuits are correctly sized.
 
You won't get much selectivity between MCBs. Check the manufacturer's tables for selectivity, or for Schneider this tool works (but only on Chrome web browser, it seems, which is crap):
https://hto.power.schneider-electri...f9fa18492b&client_id=cbt#/CheckDescrimination

Hager for the NBN series give 0.45kA limit (i.e. if your fault Zs is below 0.51 ohms then both fire).

Having said that, you won't get much selectivity with MCB - fuse either, though the Schneider tool seems a bit broken for that but from the current-time plots you are looking at 0.1kA limit (i.e. lower magnetic trip threshold of 3 * 32A for B-curve MCB)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Portsmouth
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Lighting circuit supplied from a 32A ring main socket.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Cashman,
Last reply from
Lister1987,
Replies
11
Views
5,693

Advert

Back
Top