Hi All,
I attended a welders yard today with numerous electrical problems.
Very old insatallation in poor condition, never had a PIR and no sign of any maintenance, a total mess.
Firstly they had a large 3 phase pillar drill whose metal casing went live when switched on. I found a short between a phase and earth from the commando plug which would explain the fault but why did it not blow the fuse? Old MEM DB, rewireable fuses.
Secondly they had a cooked earth cable within a control box for a large saw. Apparently, the staff told me they were welding nearby when it started to cook and it stopped when they finished welding. the commando in which the welding unit was plugged into and the saw supply are on separate curcuits.
They went on to tell me they previously had a drill plugged into a switched on 13a socket resting on a table not being used whilst on the same table they started welding, the cable from plug to drill started to burn out.
The yard is in a semi-rural location and at first glance it appeared to be a TT, as there is a tatty old approx 10mm cable running from the MET to the factory floor and is then untraceable, however there is a 10mm earth terminated into the neutral block at the head which would suggest PME. We attempted to get confirmation from the LEB as to the supply earthing type but to no avail.
I have taken loops at head, main switch, isolators and commandos and the reading are from 0.28 Ohms to 0.53 Ohms, acceptable.
I have also disconnected the suspected earth rod fly lead and taken a EFLZ and it was 1683 Ohms.
We suspect that it may have been TT originally and due to a poor earth perhaps they decided to jab into the neutral, but its not designed for PME.
To be honest really not sure.
Can anyone help is there a way I can determine the supply type?
Any help is appreciated.​
 

They went on to tell me they previously had a drill plugged into a switched on 13a socket resting on a table not being used whilst on the same table they started welding, the cable from plug to drill started to burn out.

I have seen this before, tell them to stop welding on the same table as the drill as I think it earths back through the cable. I done it with a 240v grinder that I left on the bench when I was a lad and got a bollcking for it.
 
First and most important question for you, ....Are the owners of this welders yard prepared to put all there electrical deficiencies right?? If there not and just after a quick fix here and there, ...Walk away!!! You will be up to your head in trouble if anyone gets injured after you have left.

Secondly, And i'm not being funny here, do you feel confident enough to be able to bring this installation up to a safe and decent standard?? This sounds like a can or worms that needs a fair bit of experience and know how, to bring back to any form of normality.
 
The welding kit is finding alternate route and using the ground and into the nearest earth cable it finds, this is a highly dangerous set-up as it sounds like a faulty welding set or poor connection on his out going leads, this can and has killed many ppl in the past the amount of current flowing is extremely high and with burn out any earths its tracks to, as goes the pillar drill obvious earth path fault and again could kill or injure anyone using them, you need to express how dangerous the installation is and because the welder could have burnt out various earths he needs to stop production and have an immediate pir done, there isnt any half way mark here if someone dies while your there they will say he didnt tell us to stop using anything, i would condem any items effected with warning notices and padlock off supplies till route of problem found this way they cant say you didnt tell them not to use them.
 
The welding kit is finding alternate route and using the ground and into the nearest earth cable it finds, this is a highly dangerous set-up as it sounds like a faulty welding set or poor connection on his out going leads, this can and has killed many ppl in the past the amount of current flowing is extremely high and with burn out any earths its tracks to, as goes the pillar drill obvious earth path fault and again could kill or injure anyone using them, you need to express how dangerous the installation is and because the welder could have burnt out various earths he needs to stop production and have an immediate pir done, there isnt any half way mark here if someone dies while your there they will say he didnt tell us to stop using anything, i would condem any items effected with warning notices and padlock off supplies till route of problem found this way they cant say you didnt tell them not to use them.


Absolutely what he said^^^!!!
 
As it is not within an electrician's power to disconnect any supply would it be prudent to get in touch with the DNO advise them of the potentially lethal condition of this installation and get them to come and pull the supply?
 
Hi All, they have asked for a PIR of the installation which I will be doing tomorrow. In terms of there intentions, I suspect they want to make the present problems safe but I very much doubt they will want to rectify the problems arising from the PIR which will be very costly. I would not choose to take this job myself it was kindly given to me from the company I work for. Its a 3 phase supply
 
In terms of there intentions, I suspect they want to make the present problems safe but I very much doubt they will want to rectify the problems arising from the PIR which will be very costly.
By the sound of it I'd guess that making the present problems safe and rectifying all problems arising from the PIR are going to be one and the same mate.
 
As it is not within an electrician's power to disconnect any supply would it be prudent to get in touch with the DNO advise them of the potentially lethal condition of this installation and get them to come and pull the supply?
I beg to differ, although he can isolate downstream on this occasion you are within your rights in certain situations to break a dno seal and remove supply fuses if you deam not doing so would be a greater risk of fire or safety (normally if the tails are exposed live parts etc)
 
I beg to differ, although he can isolate downstream on this occasion you are within your rights in certain situations to break a dno seal and remove supply fuses if you deam not doing so would be a greater risk of fire or safety (normally if the tails are exposed live parts etc)
I thought we couldn't do it but I stand corrected
 
When they use the welder are they running the earth return from the set to the work piece? It’s a common failing they just clip on to any old steelwork near the set and rely on what ever return path that happens to be there. Over the years I’ve had SWA’s by the dozen toasted by welding currents.
Welders are in a class of their own, they can destroy anything.
 
Last edited by a moderator:
When they use the welder are they running the earth return from the set to the work piece? It’s a common failing they just clip on to any old steelwork near the set and rely on what ever return path that happens to be there. Over the years I’ve SWA’s by the dozen toasted by welding currents.
Welders are in a class of their own, they can destroy anything.
Used to work as a welder before i got into sparkying and believe me...any loose connections/joints and they really cook when connected to welding plant....i`v seen tough insulation on heavy cable just wilt and drop off due to heat generated............
 

Reply to electrical problems at welders yard, supply mystery? in the Australia area at ElectriciansForums.net

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top