Is this your private opinion or I can find this in regs ?
411.3.3 again.

BS7671:2018 18th Edition.

411.3.3 Additional Requirements for Socket-outlets and for the supply of mobile equipment for use outdoors

In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:

(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.

An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
 
411.3.3 again.

BS7671:2018 18th Edition.

411.3.3 Additional Requirements for Socket-outlets and for the supply of mobile equipment for use outdoors

In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:

(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.

An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
Ok. So who should do the risk assessment ?
 
Ok. So who should do the risk assessment ?
A competent person. You would need to seek advice from a health and safety professional who has dealt with electrical risk assessments in the past.
 
After carrying out the Hazard Analysis if a hazard is identified to be present, then the Risk Assessment will deal with how that risk can be minimised, but why would you even consider not putting RCD protection in a workshop where IMO the risk is greater than any domestic installation?
 

Reply to 5 pin socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock