- Reaction score
- 16,753
Is this your private opinion or I can find this in regs ?
Have you got a copy of the regs?
Discuss 5 pin socket in the UK Electrical Forum area at ElectriciansForums.net
411.3.3 again.Is this your private opinion or I can find this in regs ?
Ok. So who should do the risk assessment ?411.3.3 again.
BS7671:2018 18th Edition.
411.3.3 Additional Requirements for Socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:
(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
A competent person. You would need to seek advice from a health and safety professional who has dealt with electrical risk assessments in the past.Ok. So who should do the risk assessment ?
Reply to 5 pin socket in the UK Electrical Forum area at ElectriciansForums.net