all sockets up to 32A should be RCD protected since before 18th ed. however if installed to 17th., a RA could negate the need.
 
used to be that RCD could be omitted if under supervision of skilled or instructed muppets persons. since then IET have realised that most instructed persons are muppets, so regs. changed.
 
used to be that RCD could be omitted if under supervision of skilled or instructed muppets persons. since then IET have realised that most instructed persons are muppets the manufacturers' donations to the beer fund were dropping, so regs. changed.
 
If it is a workshop (not domestic) you can still have a risk-assessment to say not needed (or problematic).

Depends on the expected use really, some 3-phase outlets should have RCD protection as used outdoors and/or with tools liable to chop cables, others it is pointless as low risk and just a cost and trip-risk for high leakage things.

Hard-wiring seems the only option there, but that makes it impossible for a non-spark to swap over stuff in an emergency, etc.
 
If it is a workshop (not domestic) you can still have a risk-assessment to say not needed (or problematic).

Depends on the expected use really, some 3-phase outlets should have RCD protection as used outdoors and/or with tools liable to chop cables, others it is pointless as low risk and just a cost and trip-risk for high leakage things.

Hard-wiring seems the only option there, but that makes it impossible for a non-spark to swap over stuff in an emergency, etc.
Is this your private opinion or I can find this in regs ?
 
Is this your private opinion or I can find this in regs ?
411.3.3 again.

BS7671:2018 18th Edition.

411.3.3 Additional Requirements for Socket-outlets and for the supply of mobile equipment for use outdoors

In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:

(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.

An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
 
411.3.3 again.

BS7671:2018 18th Edition.

411.3.3 Additional Requirements for Socket-outlets and for the supply of mobile equipment for use outdoors

In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:

(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.

An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
Ok. So who should do the risk assessment ?
 
Ok. So who should do the risk assessment ?
A competent person. You would need to seek advice from a health and safety professional who has dealt with electrical risk assessments in the past.
 
After carrying out the Hazard Analysis if a hazard is identified to be present, then the Risk Assessment will deal with how that risk can be minimised, but why would you even consider not putting RCD protection in a workshop where IMO the risk is greater than any domestic installation?
 

Reply to 5 pin socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it...
Replies
4
Views
2K
Hi, after some discussion with electricians, does removing a 16A or 32A socket constitute safe isolation? I understand that removing the socket...
Replies
8
Views
504
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
694
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock