Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it applies to all socket outlets, we have to install a 63A 5 pin socket located outside. Thanks in advance
 
411.3.3 30mA RCD shall be provided for socket outlets not exceeding 32 amps - for use by persons of capability BA1, BA2, or children; and in other locations; and for mobile equipment to be used outdoors.

But see note 3 - RCD protection for all socket outlets is recommended.
 
  • Like
Reactions: pc1966
I'm told it applies to all socket outlets,

Told by who?
If you are being told this by the person who is paying you then crack on and do what they want.
If you are being told this by someone else then ignore them.

You are right that it is sockets of 32A or less which require additional protection by 30mA RCD (RCD protection may be required for other reasons such as fault protection in a TT system)

You might decide that, above and beyond tbe requirements of the regulations, 30mA RCD protection is beneficial for your particular application, but it is not a requirement.
 
  • Like
Reactions: pc1966 and loz2754
Told by who?
If you are being told this by the person who is paying you then crack on and do what they want.
If you are being told this by someone else then ignore them.

You are right that it is sockets of 32A or less which require additional protection by 30mA RCD (RCD protection may be required for other reasons such as fault protection in a TT system)

You might decide that, above and beyond tbe requirements of the regulations, 30mA RCD protection is beneficial for your particular application, but it is not a requirement.
Thank you Dave , the reason I asked was that I was told it had been amended but couldn't find it so I was sceptical anyway.
 
  • Like
Reactions: DPG
Thank you Dave , the reason I asked was that I was told it had been amended but couldn't find it so I was sceptical anyway.
The main amendment change was that the omission of RCD protection now requires both a risk assessment and to be in use only by skilled/instructed personnel.

An example of where that is an appropriate approach is a computer room where you might have racks equipment with lots of leakage fed from 16A or 32A connectors. The room is normally secured and only staff in there would be technically qualified, also it is usually a clean, dry, and well organised/tested so the risk of a shock is low as well.
 
  • Like
Reactions: Gricey12 and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCD sockets regulation
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Gricey12,
Last reply from
pc1966,
Replies
4
Views
2,724

Advert