agricultural tt earth

Discuss agricultural tt earth in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Just been to look at a job subing to grain drying firm to help then installing cables, lighting etc. The mains is 3ph in house, across newly tarmac to a small out house were it goes to db, then off to variouse sub dbs. The main swa from house is 16mm 4 core, swa as earth. ( No 300 / 500ma main switch in house.) From here it will run to the main board to the new grain shed. There electrican says put 300ma main switch on db in grain store and make it to tt, (as they havent priced to altet anything) But I thought it should be a source. So I proposed making main swa in to tt system / eart rod / 300 ma, then all of farm protected and wont trip the current farm house. Ah this is a arable farm, no livestock ever present, am I right or totally wrong and should keep my thoughts to my self
 
Right - at the risk of an amount of ridicule, I'm now confused. I'm either had too many ciders in the sunshine or am just not reading those tables right: We've got 16mm conductors, which means we need a cpc of 1/2 16 = 8mm. We've got TN-S so we need to satisfy 544.1 and therefore need to be somewhere between 6mm and 25mm for a bonding conductor. That table says we've got a csa eq of 49mm, yes? So where's the problem?!
 
Right - at the risk of an amount of ridicule, I'm now confused. I'm either had too many ciders in the sunshine or am just not reading those tables right: We've got 16mm conductors, which means we need a cpc of 1/2 16 = 8mm. We've got TN-S so we need to satisfy 544.1 and therefore need to be somewhere between 6mm and 25mm for a bonding conductor. That table says we've got a csa eq of 49mm, yes? So where's the problem?!

There ain't one. The old boys got muggled up. The armouring of a 16mm2 4 core is sufficient as a cpc and bonding conductor but I always run a separate conductor as don't like to have to rely on a gland. (however by regulations you would be fine not to run a separate conductor- testing permitted and satisfactory results obtained obviously)
 
Right - at the risk of an amount of ridicule, I'm now confused. I'm either had too many ciders in the sunshine or am just not reading those tables right: We've got 16mm conductors, which means we need a cpc of 1/2 16 = 8mm. We've got TN-S so we need to satisfy 544.1 and therefore need to be somewhere between 6mm and 25mm for a bonding conductor. That table says we've got a csa eq of 49mm, yes? So where's the problem?!

The problem is if there is extraneous conductive parts in the grain shed . Then it requires to be the copper equivalent. So steel 8/1

ImageUploadedByTapatalk1400443342.350639.jpg
 
The problem is if there is extraneous conductive parts in the grain shed . Then it requires to be the copper equivalent. So steel 8/1

View attachment 24726

That's what I mean about not being clear on exactly WHICH csa is being used in the tables - because if some of them don't comply then that suggests they have already been converted steel > copper. And if we've got STEEL at 49, then we've only got a Cu eq of 6mm (which goes back to my original remark about using the adiabatic to see if it complies as earthing conductor or not).
 
The problem is if there is extraneous conductive parts in the grain shed . Then it requires to be the copper equivalent. So steel 8/1

View attachment 24726

That's what I mean about not being clear on exactly WHICH csa is being used in the tables - because if some of them don't comply then that suggests they have already been converted steel > copper. And if we've got STEEL at 49, then we've only got a Cu eq of 6mm (which goes back to my original remark about using the adiabatic to see if it complies as earthing conductor or not).

They are converted values!
 
Correct :)


Where did he say it was tns

Apologies..... I completely misread post #4!! Only three letters so brain scanned it as TN-S, not as typo'd TN-C-S !!!

I'll get my coat..............:dunce2:
 
Hi thanks for all comments will ask electrician on site and decide the best way. I belive he had decided to use the armourings as earth and not tt it, due to no livestock. Just didnt like saying without asking and I now have a gn 7 book to look at to see the regs. Thanks
 
There ain't one. The old boys got muggled up. The armouring of a 16mm2 4 core is sufficient as a cpc and bonding conductor but I always run a separate conductor as don't like to have to rely on a gland. (however by regulations you would be fine not to run a separate conductor- testing permitted and satisfactory results obtained obviously)

So, ....Who's got it ''muggled up'' ??

TNC-S will need the armouring to be a minimum CSA of 80mm....
 
Hi thanks for all comments will ask electrician on site and decide the best way. I belive he had decided to use the armourings as earth and not tt it, due to no livestock. Just didnt like saying without asking and I now have a gn 7 book to look at to see the regs. Thanks

As already advised you will need to pull in a 10mm separate bonding conductor, the armouring on that 4 core SWA does not comply for extending a PME equipotential Zone.
 
The csa comparisons for earthing and bonding are different.

Generally the tables you find such as that posted by Engineer54 are for assessing the compliance of a steel conductor (the armour) for use as a circuit protective conductor. in which case you are using kCu/kSt as the conversion factor, (with the associated conditions of the conductors and the csa limits).

When considering steel as a bonding conductor then you are only considering the comparative conductance of the different metals and the copper to steel resistivity ratio is 1 to 8.5 (1 to 1.68 for Cu/Al).
 

Reply to agricultural tt earth in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top