Just been to look at a job subing to grain drying firm to help then installing cables, lighting etc. The mains is 3ph in house, across newly tarmac to a small out house were it goes to db, then off to variouse sub dbs. The main swa from house is 16mm 4 core, swa as earth. ( No 300 / 500ma main switch in house.) From here it will run to the main board to the new grain shed. There electrican says put 300ma main switch on db in grain store and make it to tt, (as they havent priced to altet anything) But I thought it should be a source. So I proposed making main swa in to tt system / eart rod / 300 ma, then all of farm protected and wont trip the current farm house. Ah this is a arable farm, no livestock ever present, am I right or totally wrong and should keep my thoughts to my self
 
What is the original earthing arrangement anyway? You don't say!
 
Without knowing an overall design it's impossible to be sure, but from what you've described I would keep the TNS throughout (double check your earth conductor requirements using the adiabatic, but I'd have thought a 16mm SWA would be sufficient csa eq.) and just look at fitting RCD protection at 300 or 500mA only to locations where they may be risk of fire (think about dust etc). If the design has been done properly and discrimination taken into account then there shouldn't be any tripping issues anyway.

However........I suspect that it's probably like any other farm I've ever been on and is a real spider-web mess of DIY electrics and broken kit!!
 
Why would you make a grain house TT?? I can understand where livestock is involved.

here...some livestock:

e.jpg

keep the mice down....

you`l need to construct a faraday cage for it...
 
You do not have to go TT as no livestock will ever be about ( As long as you are absolutely positive of this ! ) , but you will need to protect everything with a RCD of no greater than 300mA ( Used to be 500mA for he 17th , but has now changed to this for the 16th ) , you could even drop this to 100mA , but as most grain handling systems are now starting to go inverter drive you may have issues with just 100mA of fault protection , and don't forget it wants to be an s-type .
As for placing it at source , in the house , or at the first shed , only you know the site conditions .
 
Last edited:
The main swa from house is 16mm 4 core, swa as earth.

Nope, using the SWA for your main earth to this grain shed is a non starter, the Armouring will not comply where main bonding is also required, it's only suitable for purposes of providing the cables CPC.... You're going to need to provide a separate earth conductor, 10mm minimum.
 
16mm 4 core is actually 49mm not 50mm, but the 50mm is as near as dam it!! lol!!


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
 
Here you go Glenn....

Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

15

16

17

2.5

5.7

17

19

20

4

9.0

21

23

35

6

13.6

24

36

40

10

22.6

41

44

49

16

36.1

46

50

72

25

36.1

60

66

76

35

36.1

66

74

84

50

56.4

74

84

122

70

79.0

84

119

138

95

107.2

122

138

160

120

135.3

(131)

150

220

150

169.2

(144)

211

240

185

208.6

(201)

230

265

240

270.6

(225)

(260)

299

300

338.3

(250)

(289)

(333)

400

403.9

(279)

(319)

467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

16

17

18

2.5

5.7

17

19

20

4

9.0

19

21

23

6

13.6

22

23

36

10

22.6

26

39

43

16

36.1

41

44

49

25

36.1

42

62

70

35

36.1

62

70

80

50

56.4

68

78

90

70

79.0

80

90

131

95

107.2

113

128

147

120

135.3

(125)

141

206

150

169.2

(138)

201

230

185

208.6

(191)

220

255

240

270.6

(215)

(250)

289

300

338.3

(235)

(269)

(319)

400

451.0

(265)

(304)

452



For CPC purposes ''ONLY''. Do not use where BONDING is also a requirement....
 
Here you go Glenn....

Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

15

16

17

2.5

5.7

17

19

20

4

9.0

21

23

35

6

13.6

24

36

40

10

22.6

41

44

49

16

36.1

46

50

72

25

36.1

60

66

76

35

36.1

66

74

84

50

56.4

74

84

122

70

79.0

84

119

138

95

107.2

122

138

160

120

135.3

(131)

150

220

150

169.2

(144)

211

240

185

208.6

(201)

230

265

240

270.6

(225)

(260)

299

300

338.3

(250)

(289)

(333)

400

403.9

(279)

(319)

467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

16

17

18

2.5

5.7

17

19

20

4

9.0

19

21

23

6

13.6

22

23

36

10

22.6

26

39

43

16

36.1

41

44

49

25

36.1

42

62

70

35

36.1

62

70

80

50

56.4

68

78

90

70

79.0

80

90

131

95

107.2

113

128

147

120

135.3

(125)

141

206

150

169.2

(138)

201

230

185

208.6

(191)

220

255

240

270.6

(215)

(250)

289

300

338.3

(235)

(269)

(319)

400

451.0

(265)

(304)

452





Ta..

here...:

have your self a likes n thanks...
:D
 

Reply to agricultural tt earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi Guys/Girls A quick question. Would I need to TT a stand alone socket detached from main building (TNCS) that could be used with a Class I...
Replies
3
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock