Short question (2006 paper):


'Small commercial unit owned by a paint company:

Supply characteristics as follows..
The supply forms a 400/230V 50Hz TN-C-S system. The main fuses are 100A BS 88-2 and measured value of PFC is 1600A. The earthing conductor is a 25mm copper conductor and the main equipotential bonding conductors to gas, water and structural steel are 16mm copper.

Determine Ze from the above information'


Remember this causing much confusion...

Answers?
 
Last edited by a moderator:
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.
 
Its a ---- question TBF. I've had a few over the past few weeks where you only get half a story and it's up to you to make assumptions.




Anyway got go to Los Santos.....
 
Last edited:
I can tell you I was told that approx 50% of students forgot the 3 phase aspect and applied ohms law to the 1600

Approx 20% went with 800


anyone else??
 
Last edited by a moderator:
I'll give it to my tutor next week and see what he makes if it. He certainly knows his onions.
 
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.


There were other questions relating to it in addition to the Ze issue
 
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.


Respect to you Lee - 80 odd views and you are the only one man enough to post up close to an answer lol

I got this wrong (not in exam but after in class where it was put up by a lecturer)
 
There should be a new qualification, City & Guilds 2399 'Initial verification and deciphering of vague exam questions'.

I've always thought their questions tend to be ambiguous and open to several interpretations in a large number of questions I have come across.
Not very helpful when you are under pressure in an exam situation!
 
Assuming that a pfc can only be measured off a singles supply one at a time them doubled by calculation. I would work it out as 230v divided by 1600a pfc = 0.14 ze
 
The problem is clearly on how the PFC was measured. Which is not clear on the question, as it says 230/400. So you either go with 230 to give 0.14, or what I am leaning with 400 which is 0.25
 
The problem is clearly on how the PFC was measured. Which is not clear on the question, as it says 230/400. So you either go with 230 to give 0.14, or what I am leaning with 400 which is 0.25
why would you go with 0.25 on 400v ? Is it because it feels better but it wrong
 
If the PFC given was calculated with root 3. Then 1600 would have to be divided by root 3 giving 923.8. Then it's 230/923.8 = 0.248

Don't remember the exam being that complicated really. So I am staying with 230/1600

Final Answer

You can shoot me down in flames now.
 

Reply to Back in the 2391 days in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
I know you’ve all be waiting in suspense for the next exciting update in this story. I promise this one will be much shorter! The OH was back at...
Replies
21
Views
4K
And learning I am ☺️ if I didn't have the limited knowledge I have at the mo I probably wouldn't give it a second thought but as I do and have a...
Replies
15
Views
4K
  • Question
DSS Distribution Sub Station ISS Intake Sub Station TX Transformer AP Authorised Person AE Authorising Engineer OHL Overhead lines UG Underground...
    • Like
    • Winner
2
Replies
41
Views
6K
  • Question
Because the supply conductor size, determines the size of the bonding conductor. Yes they do nearly always use 3 core utilising a core as the CPC...
Replies
40
Views
7K
Deleted member 26818
D
  • Question
Panel boards or busbar chamber and switch fuses to feed your dbs.
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks