So just did an EICR few problems mostly rectified. Customer wanted new CU so put in BG with RCBO just five circuits. Tests on EICR were fine except for high ohms on Zs for lighting first floor so tracking that down. All RCBO are fine except this one 32a ring final circuit. RFC tests all fine IR around 400 + Mohms. 10ma leakage with clamp on tails. So it was the end of a long day. Said I will replace the 32 rfc RCBO.
What really made me wonder is when the downstairs ring is used i.e. kettle on, the upstairs ring trips. I just can't right now formulate an approach to it. And I do seem to remember BG RCBO being quite often defective, is that true in your experience. My first thoughts were that there is some cross connection between the RFC, not that I picked that up on testing. Now I can assure you that I have not mixed up the RFC neutrals I triple wipple checked on that.
 
So Richard Burns was spot on - an N-E fault as a result of N and E reversal at a spurred socket, which was switched on (dp switch?) or switched on or off(sp switch)on the up FRC with an appliance plugged in to it using L,N and cpc?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
BG RCBO ramp test on one of them shows trip at 15ma every other one is 24 ma
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33
Unsolved
--

Advert

Thread statistics

Created
The Ghost,
Last reply from
telectrix,
Replies
33
Views
6,993

Advert

Back
Top