Has anyone used a brass gland plate to earth a line of SWA glands e.g. at a DB, and had anyone such as an NICEIC inspection flag it up as non-compliant?

I am proposing to screw a flat plate of brass onto the top of the DB and mount the glands through it with their usual locknuts, A brass bolt through the plate will take the lug of a cable running to the earth bar. I consider this to be a suitable way to earth the glands, but someone else is saying that they did something similar and their NIC man pulled him on it and demanded separate banjos or piranhas with individual flyleads.

Any thoughts?
 
Nor me - except - a pedant could argue that if when you open the packet of SWA gland and find a banjo (as you do) then 'that's how the manufacturer intends.....'.
 
In some ways it's better - fewer connections to maintain.
their NIC man pulled him on it and demanded separate banjos or piranhas with individual flyleads.
Might be a distinction between using armour as CPC and simply earthing the armour? A single cable to earthing bar from plate may have not met collective requirements for a group of CPCs.
 
Someone like to confirm what that is?
 
Someone like to confirm what that is?
Don't have BBB with me, Section 543 (can remember that nice number!) covers sharing cpc's somewhere in it - something about the highest current expected from a fault on one of the circuits. Requirements for minimum CPC size in general (as separate) need to be met too. Probably no more than you were going to do anyway.

I was more trying to convey that knowledge of CPC sharing can be sketchy as it isn't common and anything that looks unusual can easily cause an assessor to spit dummy out.
 
543.2.9 suggests this is OK to me, although I guess easily confused with 543.2.7
 
Cant see anything wrong with it, myself. Once fitted, it's solid, less complicated, room saving, easier and it's fixed to, and therefore part of, the metal enclosure. With the earth bar link, extremely satisfactory.
 
Right, good, logic prevails.
Now, supposing the plate were not brass but aluminium?
 
Right, good, logic prevails.
Now, supposing the plate were not brass but aluminium?
Or steel, even?
Installed hundreds of pyros into industrial boiler and heating control panels in the past.. without the earth tailed pots, sometimes in groups of 20, 30 or more. Imagine the work involved to banjo or even extend pot tails.
If a problem with the NICEIC, it could be just a case of regulation for today's class of workfolk and materials.

In some extreme situations, maybe one issue could be the adverse affect of different metals but, in general....? Then again, another plus point.......brass or ally wouldn't have the rust factor.
 
Given the csa of the gland plate and as long as its thicker than tin foil and conductive you should be fine.. noted we use aluminium plates often when bringing in single core phases to stop circulating eddy currents so it's a well established practice.
 
Right, good, logic prevails.
Now, supposing the plate were not brass but aluminium?
If brass glands you will have issues of galvanic corrosion in even the slightest of damp environments.

Unless you use jointing compound like Penetrox, etc, between them.

Electrically no issue if plate is of sane thickness so max current density around the earth connection is not any risk of failure!
 
I would agree that brass is preferable to aluminium on account of the risk of corrosion and the tendency to make unpredictable contact due to oxide film formation. I raised the original question because the other chap had, like me, intended the plate to provide a neat, reliable connection for his glands, and was peeved to find an NIC inspector quibbling with it, especially in the absence of a clear-cut non-compliance.

Thanks to everyone who has replied.
 

Reply to Brass gland plate for SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've been working my way through some EICR remedials in a theatre and one of them is to sort out a slightly high Zs on a submain. Thankfully...
Replies
17
Views
3K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
Help please. Firstly the kit I'm using. Wiska 607 box. 25mm knockouts. 4mm 3 core swa. 20s gland Wiska 25-20mm reducer Secondly the issue...
Replies
17
Views
5K
I’ve seen debate in the past on here about whether to earth both ends of SWA at the glands even when using 3 core with a core as the cpc. My...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock