Hi Guys,

Can someone please confirm for me the cable size required

120m length, 63 amps, voltage drop 2%. three phase. Does not have to be SWA.

I think it should be 25mm but would like a second opinion please.

Thanks in advance
 
25mm will give a VD of 11.34V. that's approx 5%.
 
Wots your cable method and is that the breaker size 63amp I take its no neutral so you using the neutral for an earth correct and wots the abiant tempter sounds right wot your saying with the lack of info god bless you with the talls and making off the SWA gland when I say use the neutral core as earth please banjo up the outer sheath and strap in down to earth

garbage like that would be more suited to the plumbers' forum, mate.
 
Wots your cable method and is that the breaker size 63amp I take its no neutral so you using the neutral for an earth correct and wots the abiant tempter sounds right wot your saying with the lack of info god bless you with the talls and making off the SWA gland when I say use the neutral core as earth please banjo up the outer sheath and strap in down to earth


Seriously, what does this mean???
 
Wots your cable method and is that the breaker size 63amp I take its no neutral so you using the neutral for an earth correct and wots the abiant tempter sounds right wot your saying with the lack of info god bless you with the talls and making off the SWA gland when I say use the neutral core as earth please banjo up the outer sheath and strap in down to earth


It's not your technical knowledge that folks are questioning.
It's the fact that you are too lazy and dis-respectful to even bother trying to post legibly.

If you have genuine problems reading and writing then I believe that there is software that can help.
 
i have to ask, " why are you aiming for only a 2% VD?"
 
bloody frogs, trust them to be awkward.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Was France but now Essex

Thread Information

Title
Cable calc verification please
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Victor,
Last reply from
Victor,
Replies
17
Views
2,044

Advert

Back
Top