Hi, I wanna know if I can incorporate a few outdoor sockets in to the same ring that will be feeding all the internal sockets, or does it have to be seperate - internal/external
 
No problem having external sockets off of internal circuit, so long as the circuit has 30mA rcd/rcbo & correct IP rating of external sockets is observed.
 
Just installed one of these today. Basically I put a metal clad Rcd protected double socket in a shed. Connected with a 2.5mm ammoured cable going from a Fused connection unit off his main ring.

regards Luke (Admin)
 