As above, came to commission a circuit yesterday and got to the last step (test the RCBO) and on 3 attempts the main RCD went instead. TT installation, no markings on front of RCD but assume must be 30mA non time delay.
The obvious answer is quote them to swap for a type S RCD but it's a big 3 phase one and will be expensive!
My main problem is what to do about certificating? I've commisioned the circuit as everything else tested fine and even if the RCBO I've put in was faulty it still met disconnection times because of the main RCD tripping.
It's a 6A lighting circuit. Strangely enough there are loads of other RCBOs on the board too so I can only assume that these either haven't been tested or someone bypassed the main RCD to do them!
Surely a pre-change survey highlighted that an RCD was already fitted and you would have noted the type etc? I guess customer will be ****ed off at having to fork-out for more work?
Just fudge the cert, cheat, lie, else like plenty of other sparks don't send them the certificate. That should avoid the problem :)
Sounds like the up-front RCD isn't 100mA time delayed?
No need to cheat or lie , just write a note in the " Comments on existing Installation" box saying something like ;
Unable to complete Rcbo tests due to unsuitable main switch device not providing discrimination to downstream devices.
Well its the truth aint it ? lol
^^^ Yeah, Apologies. Bit fed up with the industry today. A combination of the **** Part P theme and a local 'electrcian' advertising as an NICEIC spark when he isn't :( Why cant people just do work properly, or not at all?
The above wording is good.
Thanks all. Only got a quick look at the board prior to the work and as recent we assumed by the number of 30mA RCBOs in there that the main RCD was a 100mA type S. Clearly it isn't :S They've just had the PIR too so this obviously wasn't picked up on which is strange (as they noted other things on the same board).
Also there's about 20 circuits in total so an RCBO was specced to avoid knocking the whole building out.
Will note on the cert that not possible to test like you say and recommend having it changed. NIC assessor is out in a few weeks so might stop off at this one to see what his take on it is.
Thanks again
Edit: Other option is to swap to a breaker I suppose and put down the test results for the RCD already in place, loses the discrimination between circuits but the paperwork would be better.
Tell the customer there is a problem with the installation and note it as biff has suggested. Then give them an idea of the costs to change the main RCD for one that will provide the necessary discrimination and inform them that it should have been picked up on the EICR(PIR).
if all other circuits are RCBO, change that main rcd for main switch, that will then let the RCBOs operate how the customer wants them to ( i.e if one trips it doesnt knock other circuits out)
On a TT?!?!?
Either S type upfront, obviously this will cost them....
Or if there is a 30mA upfront take the rcbo out as you are just putting two 30mA in series which is senseless LOL...
Your just fed up with that today...?? :p
Just a thought...I assume that the testers check an rcd by leaking current to cpc. So, you could then test the rcbo by connecting the cpc end of tester to the neutral on the supply side but before the rcd. Only the rcbo would trip as the rcd would not detect any leakage. Or am I missing something?
They create an imbalance, they don't leak current.
Its pointless even testing it really if one trips first.
Layout of rcds needs sorting 1st IMO.
I know megger had some issues with certain rcbos, where reversing lead connections could solve problems, i know its not a megger but may be worth a try lol
1) Establish by testing by ramp or device enquiry the upfront RCD type 100/30mA TD ?
2)If the upfront is 30 mA why would have other peeps fitted 30mA RCBO's ?
3) If all circuits on board are individually 30mA protected there is no requirement to have a 100mA up front, only if some are not.
4)You state the up front meets the disconnection times ? what on x1 ? and/or x5 ?
5) Establish the characteristics of the upfront, make sure it meets the regs, bridge out and test your RCBO, note the findings on the cert.
Your the last one to work on the board..It's your --- on the line if someone gets an --- winder mate do it once do it right !
Just cos he's the last one to work on the board doesn't mean he's responsible for it all!
Only what he's put on his cert in the extent.
Agreed..BUT the OP suggested that he wouldn't test HIS RCBO and rely on an RCD ( One by his own admission he can not identify ) to give additional protection, so he either has to falsify the cert or investigate ? Failure to investigate would make him liable sorry
Im sure if the consumer unti is metal clad or in a metalic enclosure it has to have an up front RCD ,
Nick I will swot up but I believe the the enclosure needs to be insulated with additional mechanical protection to the tails have a peek at the green OSG page 30 Figure 3.6.3 (iii)
You would need a Rcd for additional protection if metal, as if a tail was to touch the metal db sufficient current could not flow to operate the ocpd (DNO fuse).
Additional protection to tails by another means is fine just hard to do.
I'd go with plastic enclosure and Rcd
OSG states insulated enclosure OR extra protection what are tails going to short on passing through a plastic enclosure ? Not critising the value of the suggestion better to be safe than sorry, just the need of it
J
Reply to Can't test RCBO as main RCD trips first - what to do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks