Hi Guys New guy here can someone advise me what is the maximum earth continuity reading allowable on a lighting circuit which is protected by a 5 amp fuse and has about 100 mts of 1.5mm T&E utilised
 
you mean max ZS????

and im assuming by 5a you have BS 1361 fuses

it is 10.45 ohms


or if its BS 3036 fuses

it is 9.58 ohms
 