Guest viewing is limited
B
besenzig
Running a 20A 6.0mm T&E radial to utility room to supply two single 13A sockets to feed Washing Machine and Tumble Dryer.
The T&E will be terminated in a PVC adaptable box, just wondering how to make the connection to the sockets as terminals
will not take 6.0mm.
Can I use connector strip using 4.0mm or 2.5mm to feed the sockets, was hoping to use Wago but they too will not take 6.0mm.
Is there connector out there that will do the job.
Could I ask why you are using 6mm cable Besen?
2.5mm would be the cable to use, and Wago do make connectors that take 6mm.
Cant seem to find them, would you be able to supply a link. 6mm is already there, originally intended for garden shed but unused so using it for utility room. Over engineered i know but its there.
Done exactly that before, existing 6mm supply repurposed for a dishwasher, washing machine and tumble dryer just used 3 single Mk socket they take 2x 6mm don't mess around with additional connectors to drop the cable size
As already said you can get a twin terminal socket for each conductor. If not go for the MK single termination socket. I've got 2 lots of 6mm in before without giving them a hair cut lol. Below is the MK tech spec for a singe termination socket.....
Terminal capacity:
Live, neutral & earth
3 x 2.5mm2
3 x 4mm2
2 x 6mm2 (stranded)
2x 6.0mm conductors will go into an MK socket no problem,but as previously stated they need to be cut square and stripped carefully. Insert into terminal as stripped,dont twist the cores up.
Also dont fit the standard lazy a-rse 25mm flush back box,35mm minimum....45 even better.
It is difficult to stick 2 6mm2 cables into a socket, however the whole thing is wrong. Assuming the 6mm2 is already in place and therefore the OP intends to use it the best method would be a double socket rather than 2 singles, job done, move on LOL
That maybe bonkers but toatly possible MK sockets will accept 2x 6mm no problems. I also used single sockets so each machine has it's own socket so 2 plug tops are not connected to one Double socket
You may get 2 X 6mm2 conductors into the terminals, but how will you get the single socket back against the pattrice LOL
Well I'll take your word for it, however I still hope I never come across 2 x 6mm in the back of a socket! Ugh and on a 25mm box as well, no ta!
With you there, that would be a bad design and a bodge up, thats why I sugessted one twin socket rather than 2 singles so only one 6mm2 conductor is needed, that said after seeing murdochs reply I am now on the side of a small DB
Come on Gaz, to attempt to stick 2 6mm2 in a single socket when there is no need to is just plain Daft IMHO, and I suspect others will agree as well, have you been at the christmas sherry already?
You can use a 35mm deep box no problems and what exactly is wrong with having a 6mm radial instead of a 4mm or even 2.5mm
As long as you terminate the cable correctly and dress the cables back there's no problem
I am not suggesting it cannot be achieved, I am suggesting it is a silly way to make an appliance work under the circumstances mentioned in the OP, the design is poor.
Connecting 6.0mm T&E
besenzig,
Deleted member 9648,
