Hello all,
I've got an unusual fault on a cu main switch in a Wylex split load board. I was called to a property with no power. The main switch was in the off position and both rcds and all breakers were in the on position. There was a leak on the toilet but no water through the electrics. Checked it over and switched the main switch back on.
I was upstairs with the plumber when 5 minutes later power goes off and main switch had dropped again. Switched back on, went back next day, checked property, changed main switch for new one, polarity correct, Ze 0.28, PFC 0.83, ins res >299 on all circuits except down sockets which was 154. Ramp test 27 Rcd test 28/13 on both rcds.
Question was asked if anyone had switched main switch off which didn't go down very well. Property was solar panels. Never come across this before, any guidance would be most helpful.
 
The board and original switch were wylex, switch replaced with crabtree from van and fault reappeared in the morning. Unsure if switch was new so replaced with another Crabtree switch robbed from a new consumer unit and also same fault. So according to customer same fault on three different switches. All switches felt as though they were operating well.
As said before the customer was asked if anyone could be switching it off without her knowing and wasnt happy I'd asked the question.
 
It's in a cupboard at front door between stairs and kitchen. Husband and wife and two teenage girls.Called out last night again customer said when power went off everyone was in lounge eating Chinese. No one else in the house. Ghosts have been mentioned!!!!
 
They are taking the mick, as a few members have said already they do not trip out, so someone is switching them off and to even let the idea that you have had 3 faulty switches in a row enter your head is just daft, You are being led up the garden path.
 
It's in a cupboard at front door between stairs and kitchen. Husband and wife and two teenage girls.Called out last night again customer said when power went off everyone was in lounge eating Chinese. No one else in the house. Ghosts have been mentioned!!!!

It could be something less sinister and the wife may fancy you!! are you wearing aftershave or lynx deodorant when you attend site.
 
I once got called back to a house to a chandelier that ceased working the day after I had been round to install an oven and replace a RCD. It was on the way home so I popped in to have a look.
Turned out the householders "mate" had been round and unscrewed all of the bulbs so they were just sat in the shades for a joke.
 
I haven't seen one that switches itself off, let alone 3. I have seen one with heat damage that was stuck on but it was quite obvious. Any chance you can fit one of em at home?
 
Remember seeing a few threads about this on here (my thoughts were RCDmain switch) but a competant electrician would see that.
Main 100A switch tripping - http://www.electriciansforums.co.uk/threads/main-100a-switch-tripping.110396/
The thread never got updated in the end

So =
Faulty main switch
Dont believe in spooks so thats out
Idiots switching down (as the old switch used to be down)

As the switch has been changed it seem likly to be one of the other options. Never seen one turn off seen them burn open or shut but switch position is usually on.
 
I know main switches need to be physically moved. I just thought am I missing something blatantly obvious. Doubt starts to creep in. Rcds trip, main switches don't. No damage or heat to any parts of CU.No other reason than persons moving switch. It's a tenant so call outs don't cost them.
 
This'll stop them messing about with it.

echo switch.jpg
 
I know main switches need to be physically moved. I just thought am I missing something blatantly obvious. Doubt starts to creep in. Rcds trip, main switches don't. No damage or heat to any parts of CU.No other reason than persons moving switch. It's a tenant so call outs don't cost them.

It may not cost the tenant but I presume you're charging the landlord, It could be they have a gripe with the landlord and are just trying to make life expensive for them or inconvenience them.
 
Turn the switch back on. carefully add some engineers blue to both sides of the switch toggle.
When called back inspect all the fingers in the house. The answer will become clear.
Bugger to get off that engineers blue.
 
Update on "faulty" switch. One of our contractors had been to this the week before, same story main switch dropped he reset it and while upstairs at leaking plumbing power goes off and main switch down again. Will speak with management and let them make the decisions but maybe tamper label is the way to go. Tenant is gonna be good when she hears that.
 
If the tenants are genuine then ask if you can set a camera up in there to try and solve the mystery, If they have nothing to hide then they should be as eager to resolve it has you are.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
CU Main Switch fault
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
meggermate,
Last reply from
sparkdog,
Replies
37
Views
3,701

Advert

Back
Top