Our toilet extractor has, or so I thought, been failing (delayed startup, bit intermittent) for some time, and yesterday it finally stopped working. Vent-Axia Silhouette 100T.

It's going to be a bit of a pain to replace, so I though I would check the connections first just in case. Imagine my surprise when I put a meter on the incoming supply to find the live read 2.45v rather than 240v, and the switched-live some silly low reading I can't even remember. I thought my meter was broken, but I tested it elsewhere and it is fine. The lights in the toilet work, and the light switch controls the fan as usual. The switch (not a dimmer) is a simple MK single in/out wire, so I assume there must be a junction box somewhere in the ceiling, but if so that will not be easy to get to.

As an aside, would an Xpelair C4 or envirovent Silent-100 be better than another Vent-Axia should it need replacing? I would need a "plug-in" replacement due to cable placement etc.

Any help, ideas, or suggestions would be much appreciated.

Henry
 
If the live to earth voltage is same or similar to the live to nuetrual voltage, you have a fault in the live conductor path.

If not, then probably a neutral fault.
 
First thought I had when I woke up this morning was "it's probably a problem with the neutral" :blush:
If the live to earth voltage is same or similar to the live to nuetrual voltage, you have a fault in the live conductor path.

If not, then probably a neutral fault.
Hadn't tested live to earth - will do that today.

Really appreciate the advice from those who know, rather than my best guesses.

Keep well, keep safe.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Curious problem - no power to switched toilet extractor fan
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
henryg,
Last reply from
henryg,
Replies
5
Views
1,482

Advert

Back
Top