I don't see how an unbalanced load could damage a CT. Can you give us a circuit diagram and more information on the damage to the transformer?
 
IPA1 DG-A Current Transformer.jpgDG-A CT.jpgDG-.jpg
Generator is 350 KVA and usual load about 50% but recently disbalance appeared probably because load bank failure, we observed difference in phase current and it were about LI-200A L2-200A and L3-100A and burned transformer was on phase L3 reviled it later after ACB trip by multifunctional relay.
 
Thanks Elena and what do you think could reason of CT damage?
Existing current transformer manufacture ‘’Frer’’ type TA0008800K01 Ratio 800/1 A 0.72-3kV 5P15 M0503 resistance secondary winding 11 Ω but failed CT was 5.6Ω
 
Last edited:

Reply to Current transformer damage in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock