Hi all - been an idiot / schoolboy error - drilled into a wire that drops down to a fused spur socket in the kitchen (for washing machine I think) - blew 30A fuse for downstairs sockets and tripped RCD. The wire is behind plasterboard.
Any advice on what the repair should be would be appreciated before I call someone in.
Any idea what this should cost?
 
  • My first reaction is always make the joint meet or exceed the OCPD, so 32A is bound to be OK.
  • Another way of looking at it, is to make sure the joint is not the weakest link. If you look at 2.5mm T&E CCC (such as Table 7.1(iii) in the OSG) then it is not more than 27A, so that would be another option.
  • However, the real question is what is needed for RFC leg rating? As @Pretty Mouth has already listed it is explicit in regulation 433.1.204 but you could deduce that from looking at the acceptable methods for a 2.5mm RFC, which are (from OSG Table 7.1(i) on page 75) methods 100, 102, A & C, and of those the lowest rating is method 'A' at 20A.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wakefield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Drilled into wire in kitchen
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
Dave H99,
Last reply from
pc1966,
Replies
30
Views
4,316

Advert

Back
Top