skimmed through but agree with preceding posts. copper pipes under sink and bath, if preceded by plastic, are not extraneous and should not be bonded. the sparks who suggested this should be taken out and shot in the goolies, then sent on a course to understand the purpose of bonding. it seems you have an underlying fault which manifested iteself due to a water leak. sack both electrician and plumber, and then get an expert in each field to fix.
It is entirely possible that there is no fault with the electrics, a ceiling rose could be wired with no permanent live, even if it has a permanent live, the switched live is normally on the outside of the rose.
Any water creeping into the rose is likely to contact the switched live far before the permanent live. Tracking back through the wet woodwork in the house until it finds a path to earth.
If there is an rcd supplying the circuit, the path to earth through the timber and back to earth via multiple paths is going to trip the rcd well before any risk of shock occurs.
The simple fact is, the system installed because of its age is unable to detect the type of fault that occurred.
Modern rcd’s Or rcbo’s would have turned off the power, probably before the shock risk was there, but certainly the moment a shock was felt the power would be switched off as the device would trip in less than 0.03 seconds (less than a blink of an eye to the layman)
No wet floor (can't remember about bare feet)
No one got a shock until Sunday night but I worked out you only got a shock if the hallway light was on so maybe Friday and Saturday we happened to not use the taps when the light was on.
The shock happened if you only touched 1 tap
I had something not too dissimilar, a story I’ve recanted here many times. Long story, shortened. Complete bathroom refurb. Plumber was getting shocks when touching copper pipes and newly plastered wall. All walls in vicinity of bathroom had voltage to earth. Sometimes rcd would trip. Turns out previous owner had installed some dado rail on the landing years previously, with nail just nicking cable (stripper) to landing light.
As already said, get a competent electrician in to do some testing.
Awful read that ?. Wonder if that was a factor in RCDs to all circuits Buried less than 50mm in the building fabric coming in not long after? Shows the importance of IR testing.
but that wouldnot have identified the fault as the metal rack was fitted after the installation had been completed., and the fault was not there before.
That was a different case - the linked story involved cable damage at the time of construction, which had subsequently been certified as safe.
mybad. mixed up the 2. however, in the emma case, it seems that the fault was from cable to encosed metal stud that was not earthed/bonded. so a IR test would not pick it up.
My advice, as per other posts, get a proper electrician in to do an EICR and mention also the problem you experienced during the flood. Installing supplementary bonding will not solve the issue, (and as stated, may potentially make it more dangerous) the fault will still remain.
Speculating on what or not what it could be is no help to you. Over the years Most of us experienced sparks have come across similar faults before , (I know I have) and the faults have been identified as the same or similar to each of all the above mentioned so far, so yours could be anyone of them or something entirely different.
I would also recommend a consumer unit upgrade, modern consumer unit devices offer much better protection.
Indeed, even if you carefully followed every detail in guidance note 3 the defect would go unnoticed.
Reply to Earth Bonding In A Bathroom in the UK Electrical Forum area at ElectriciansForums.net
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Hi everyone, I am a removal man and I build office furniture. The company that I work for has based me at one of there clients buildings which...
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...