Hi there this is been happening in a few houses now I've been testing and im
a little confused, when testing my ring continuity my earth hasn't been the standard 1.67x bigger than live and neutral when using twin and earth 2.5 cable, what causes this? There is no chrome fittings or that so that wouldn't effect any earth readings just standard white plastic, today my neural and lives were 0.8ohms but my earth was only 0.6ohms which is well short, any ideas guys and can someone point me in the direction for the forum app as I can't find it anymore, thanks
 
Hi there this is been happening in a few houses now I've been testing and im
a little confused, when testing my ring continuity my earth hasn't been the standard 1.67x bigger than live and neutral when using twin and earth 2.5 cable, what causes this? There is no chrome fittings or that so that wouldn't effect any earth readings just standard white plastic, today my neural and lives were 0.8ohms but my earth was only 0.6ohms which is well short, any ideas guys and can someone point me in the direction for the forum app as I can't find it anymore, thanks

Any parallel earth paths that are still connected?
 
No metal conduit, just standard twin and earth clipped, it's happened a few times now and was wondering if anyone had any ideas? Could it be down to if the earths are twisted quite a lot at each socket ?
 
The fact that the earth conductor has a lower resistance than the line and neutral in T&E, suggests that there are high resistance joints on the line and neutral conductors.
 
The fact that the earth conductor has a lower resistance than the line and neutral in T&E, suggests that there are high resistance joints on the line and neutral conductors.

Thats what I was thinking but for both live and neutral to be slack the exact same amount to give the same reading I thought was unlikely ?
 
Agree with Spinlondon actually, that was my first initial thought
Really. 2 conductors of the same size having matching poor terminations to give identical readings...... so say both incorrect, based purely on the fact that cpc end to end is lower than expected value. Lottery odds that one. Obviously parallel earth paths.
 
Really. 2 conductors of the same size having matching poor terminations to give identical readings...... so say both incorrect, based purely on the fact that cpc end to end is lower than expected value. Lottery odds that one. Obviously parallel earth paths.
Not quite as clear cut as that, I think 'more likely to be' would be a better description.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth continuity
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
46

Thread Tags

Advert

Thread statistics

Created
nicsin02,
Last reply from
cprfenom,
Replies
46
Views
8,621

Advert

Back
Top