any advice what code to put here if CU looks ok but unsure if the wall it's mounted on, is fire rated?
 
4.4 in an EICR relates to regulation 526.5 which relates to the enclosure (i.e the CU) not what it is attached to. So if you are saying the 'CU looks ok' (i.e it meets the requirement of the above reg) then I cant see it requiring a code for 4.4 of the EICR.
 
4.4 in an EICR relates to regulation 526.5 which relates to the enclosure (i.e the CU) not what it is attached to. So if you are saying the 'CU looks ok' (i.e it meets the requirement of the above reg) then I cant see it requiring a code for 4.4 of the EICR.
it goes hand in hand with the IP rating

has the IP rating been compromised (this would include ill fitting fronts etc)...

if not then it could also be said that the fire protection is intact

be sure though as well to verify that the dis-board and any associated equipment is good for any external influences....caus theres a tick box for that as well...
 
question was theoretical, but that was what i was wondering, if CU is mounted on untreated wood or non-fire rated plaster board , possibly with a large hole in back of CU for cables to enter, does this compromise integrity of CU in regards to fire rating standards? if so, possibly a code 2?.

...I'm starting a lot of domestic EICR's shortly...possibly treat wood with a fire retardant and fill hole with a fire rated filler?...

...or am i taking this too far? lol
 
If like the majority of domestic CU's it's made of plastic, it's going to end up as a molten blob on the floor no matter what you do. That's whether the heat is generated within the CU enclosure or externally via a fire. In either case the plastic the CU is made from, will generally be fire retardant (eg it won't burst into flames) to some BS standard or other...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR - 4.4 - fire rating of CU - code rating?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Silk6911,
Last reply from
Engineer54,
Replies
8
Views
3,332

Advert

Back
Top