Discuss EICR - 4.4 - fire rating of CU - code rating? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
4.4 in an EICR relates to regulation 526.5 which relates to the enclosure (i.e the CU) not what it is attached to. So if you are saying the 'CU looks ok' (i.e it meets the requirement of the above reg) then I cant see it requiring a code for 4.4 of the EICR.
it goes hand in hand with the IP rating
has the IP rating been compromised (this would include ill fitting fronts etc)...
if not then it could also be said that the fire protection is intact
be sure though as well to verify that the dis-board and any associated equipment is good for any external influences....caus theres a tick box for that as well...
question was theoretical, but that was what i was wondering, if CU is mounted on untreated wood or non-fire rated plaster board , possibly with a large hole in back of CU for cables to enter, does this compromise integrity of CU in regards to fire rating standards? if so, possibly a code 2?.
...I'm starting a lot of domestic EICR's shortly...possibly treat wood with a fire retardant and fill hole with a fire rated filler?...
...or am i taking this too far? lol
If like the majority of domestic CU's it's made of plastic, it's going to end up as a molten blob on the floor no matter what you do. That's whether the heat is generated within the CU enclosure or externally via a fire. In either case the plastic the CU is made from, will generally be fire retardant (eg it won't burst into flames) to some BS standard or other...
Reply to EICR - 4.4 - fire rating of CU - code rating? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...