Been to a property and been asked to add a socket in Bradford City Centre

Just to give you an idear of the system hear goes..

Connecting meter to DB is 10mm twin and earth with a main service fuse of 40 Amp

DB this is the first time I have seen a db like this, MCB type things but the are not removable. Council sticker saying install board fitted 1992

NO rcd's on any circuits, One socket located at rear door that has the potential to feed portable equipment outside

Main bonding present only

Insulation resistance 4.2M oams on full installation

External Earth fine, Loop impedance for all circuits satisfactory, Continuity of CPC to all points and ring is wired on a ring with no spurs

Due to the IR results the age of the wiring and the house being a shell i have given 2 quotes, Rewire, New Dual RCD board. but the want only the socket fitting, I am insisting that the rest of the bonding is brought up to date and that the additional socket is RCD protected and the one near the door as a minimum.

What else would you guys be insisting on before you touch an install or what do you guys look for prior to quoting?
 
Last edited by a moderator:
What are you doing installing a socket or a EICR?

Sent from my GT-I9300 using Tapatalk 2
 
Just a socket. Advised on EICR but didnt want to pay. Just had visual and few tests
 
it doesnt need a rewire does it ?
over 4 meg on a global IR is not bad actually and you've already confirmed continuity and Zs are ok.
they only want a socket but you've quoted for rewire , bonding and Cu change ???
even dick turpin didnt have that much front lol.
 
Why advise a EICR. As long as your work meet current and any circuit you alter is safe to do so then no problems what so ever. Also make sure all ECP is bonded and main earth is satisfactory.

Sent from my GT-I9300 using Tapatalk 2
 
I apreciate 4.0 is a pass but when the house is a shell and ready to be plastered and decorated then I give the option but inform that at present the wiring is satasfactory. Cant say fairer than that. As for changing a board it saves the supplementary bonding due to no RCD's and moves the install forward as apossed to back in the edition of the regs.
 
I think the phase was "I want my electric checked" but when we talked figures that were not as keen. I agreed to 30 mins with megger and a few basic tests
 
So £400 DB change, and £70 to install a socket. Why does it need supplementary bonding? You installing the socket in the bathroom?

Sent from my GT-I9300 using Tapatalk 2
 
Regardless of what work is being done bonding arrangements need to be up to scratch and as there is no RCD then supplementary bonding is needed as per reg 132.16. Or is it not? Or is the sparky I served my time with too cut up on the regs and the guy from naspit
 
The nloke is trying for a DB change for no real reason so may as well charge prices to get Domimic Littlewood intrested

Sent from my GT-I9300 using Tapatalk 2
 
(1rcd Socket) £70 for rcd socket and updating supplimentry bonding or (RCD everything) £200 for RCD board socket and tails... Im bamboozled to think what is wrong. Ive explain what my findings are and what the costs are. Its there call from there. forgive me if I am wrong but surly we should be advising to make to install safer and moving forwards in the eddition of the regs and not backwards.
 
Of course we should. But also only works you carry out have to meet current regs not the whole installation. Main earthing and bonding exempt obviously as that must meet current regs.

Sent from my GT-I9300 using Tapatalk 2
 
There is no requirement for earthing and bonding arrangements to meet current Regulations.
The requirement is to ensure the earthing and bonding arrangements are adequate for the safety measure applied to the addition or alteration.
What is the intended safety measure to be applied to the new socket-outlet, and how exactly does supplementary bonding affect the safety measure?
 
My bad Spin is correct (again) my terminology isnt great

Sent from my GT-I9300 using Tapatalk 2
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR Report and defects. What is needed in order to complete minor works ???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
Djlelectrical,
Last reply from
Welchyboy,
Replies
20
Views
3,298

Advert

Back
Top