Just writing up an EICR I did today, got a long garden with SWA feeding shed at bottom, armoured not earthed (code 2) but I also noticed for part of it's run, near the veg patch, the SWA is lying across the ground. It doesn't meet 522.8.10 so I'm guessing code 2 and a recommendation that either I drag it out and cleat to fence or I get my spade out again.

Anyone got any thoughts on a code?
 
Last edited:
Which one? To my mind the lack of earthing is a 2 because if someone sticks a spade through it the armoured is not earthed and the cable sitting above the surface is possibly a 2 because of the likelihood that you could stick a spade through it and that it doesn't meet 522.8.10 which says it should be buried at sufficient depth to avoid being damaged, although it doesn't mention laying across the top.
 
I agree jdm the actually wiring only needs to be earthed at one end of the swa has a separate earth in it
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

robd

Arms
-
Joined
Location
East Anglia

Thread Information

Title
EICR SWA not buried.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
robd,
Last reply from
richy3333,
Replies
28
Views
5,480

Advert

Back
Top