Hi all. Doing a PIR on a 2 story house converted to offices. The fire panel is fed direct from cu which is very close ,( no fused spur). If it is wired in FP and on its own unprotected mcb is this ok. Would the mcb need to be locked on? Thanks
 
Hi all. Doing a PIR on a 2 story house converted to offices. The fire panel is fed direct from cu which is very close ,( no fused spur). If it is wired in FP and on its own unprotected mcb is this ok. Would the mcb need to be locked on? Thanks


I'm not sure, i can make out what your so conserned about?? Also, what do you think a ''locked on'' MCB would achieve??
 
and then what would happen if there were a fault ?
 
Hi.Yes granted.I am looking for advice on the way the panel is supplied is ok or not.Thanks
 
As far as i can see, ... it's fine!!! ...Just don't lock the breaker in the on position!!!


Tel, ...the MBC will still trip locked on or not...
 
As far as i can see, ... it's fine!!! ...Just don't lock the breaker in the on position!!!


Tel, ...the MBC will still trip locked on or not...
silly me. blonde moment caused by lack of alcohol.

i would prefer to see an unswitched FCU alongside the fire alarm panel, simply so as the alarm engineer would not have to access the DB to isolate the panel.
 
Last edited:
silly me. blonde moment caused by lack of alcohol.

i would prefer to see an unswitched FCU alongside the fire alarm panel, simply so as the alarm engineer would not have to access the DB to isolate the panel.

Sounds like the CU and FA panel is in the same location or very close to each other. Yes a dedicated FCU would have been a better option, but i can't really see a problem with this set up.
 
can't see any contravention of regs. panel has local isolation. just not usual practice
 
Been reading this thread looking for info.Working on site today and have been asked to change a fused spur to a red fused spur with neon,and a lock for mcb that supplies the fire alarm.The comissioner of the panel has asked for this.Is he going over the top.All labels are quite clear to show what is what.

6amp mcb,5amp fused spur at meter position and fused spur at fire panel about 15mtrs away.All labels in place.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Fire panel supply
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
amicus,
Last reply from
TALK,
Replies
10
Views
2,112

Advert

Back
Top