Hi
I have a Horstmann e7bx water heater boost controller for my immersion heater which I want to replace with a timeguard trtd7n timer which is suitable for dual element ,the only problem is that the new timer has only got 5 connections and old one has 10,is this possible or do I have to get another timer with the 10 connections?
Thanks
 
The two controllers you mention are designed to perform slightly different functions.
My understanding is the e7bx you have is connected to both your normal rate daytime supply, and also your cheap rate supply, and provides the ability to manually switch immersions and give a boost function. It does not itself contain a timeswitch but relies on the meter cheap rate timeswitch.
So daytime rate and night rate supplies in, and connections to the immersions out.

The proposed replacement is itself a timeswitch, and can control two immersions, but it only has one permanent supply in.

It depends on your supply and billing arrangements as to the viability of the swap. You would need to connect the new timeswitch to your normal rate supply for the clock to run all the time, so the question is - if you consume power during the cheap rate period from your full rate supply, are you charged at the lower rate? In which case you could wire the new timeswitch thus, and ensure the clock 'on' and 'off' periods are within your suppliers time periods.

Then you will have a live cheap rate supply cable that now has nowhere to go in the new timeswitch!

Sorry for the verbose reply!
 
Thanks for taking the time to reply,on the consumer unit their are 3 supplies,1 for storage heating,1 for convectors and 1 for the immersion,so I take it that the cheap rate would apply to the storage heating and the immersion,from that I can take it that if I want a permanent supply for the timer it would be at the more expensive rate,I believe you can get one with the 10 connections that can be connected straight to the E7BX but am not sure which one it is.
Thanks again
 
Thanks for taking the time to reply,on the consumer unit their are 3 supplies,1 for storage heating,1 for convectors and 1 for the immersion,so I take it that the cheap rate would apply to the storage heating and the immersion,from that I can take it that if I want a permanent supply for the timer it would be at the more expensive rate,I believe you can get one with the 10 connections that can be connected straight to the E7BX but am not sure which one it is.
Thanks again
Usually, Economy 7 tariffs apply to all circuits from 12-7 (or whatever the local version is), so that anything running overnight like a washing machine takes advantage of the cheap rate. The specific cheap rate circuits to storage heaters etc. are hardwired just to ensure they only work when the meter is in 'cheap rate' mode.

If that's the case, then the new Timeguard would work as long as the timer was set so that the off peak load was only active during the 'cheap' rates, but you'd be relying on the Timeguard timer, not the meter.

You'd also need to safely isolate the other off peak cables in the current timer, since they would become live at the same time.

Is the existing Horstmann faulty? (You can still get them) or is there another reason for changing it to the new one?

Generally the simplest setup I've found for E7 immersions is for the lower (off peak) immersion to be wired directly from the off peak supply via a DP switch which is usually left on and will heat up only when the meter is in cheap rate.

Then either another DP switch for 'boost' mode, or if preferred, a boost timer, which shuts off after 30-60 minutes to avoid forgetting to turn it on.

Normally, the only time a combined timer/controller with connections for both immersions is needed is if there is only one permanent live feed to the immersion cupboard, so that the cheap rate immersion has to be switched to match the cheap rate times.

Hope that hasn't confused you further...
 
Immersion Heater
Thanks for taking the time to reply,on the consumer unit their are 3 supplies,1 for storage heating,1 for convectors and 1 for the immersion,so I take it that the cheap rate would apply to the storage heating and the immersion,from that I can take it that if I want a permanent supply for the timer it would be at the more expensive rate,I believe you can get one with the 10 connections that can be connected straight to the E7BX but am not sure which one it is.
Thanks again

Usually, Economy 7 tariffs apply to all circuits from 12-7 (or whatever the local version is), so that anything running overnight like a washing machine takes advantage of the cheap rate. The specific cheap rate circuits to storage heaters etc. are hardwired just to ensure they only work when the meter is in 'cheap rate' mode.

If that's the case, then the new Timeguard would work as long as the timer was set so that the off peak load was only active during the 'cheap' rates, but you'd be relying on the Timeguard timer, not the meter.

You'd also need to safely isolate the other off peak cables in the current timer, since they would become live at the same time.

Is the existing Horstmann faulty? (You can still get them) or is there another reason for changing it to the new one?

Generally the simplest setup I've found for E7 immersions is for the lower (off peak) immersion to be wired directly from the off peak supply via a DP switch which is usually left on and will heat up only when the meter is in cheap rate.

Then either another DP switch for 'boost' mode, or if preferred, a boost timer, which shuts off after 30-60 minutes to avoid forgetting to turn it on.

Normally, the only time a combined timer/controller with connections for both immersions is needed is if there is only one permanent live feed to the immersion cupboard, so that the cheap rate immersion has to be switched to match the cheap rate times.

Hope that hasn't confused you further...
Thanks again for taking the time to reply,the only reason I am changing the switch is that, I only need the hot water from the immersion in the morning,it only takes about an hour to heat the water and I do not want to have the immersion on the whole night just to get hot water in the morning,the problem with this switch is that it does not have a timer on it,it has a boost timer but that has to be switched on manually which means I have to get up early to switch it on,go back to bed then get up an hour later,is their another solution to this, other than changing the switch?
Thanks again
 
Immersion Heater



Thanks again for taking the time to reply,the only reason I am changing the switch is that, I only need the hot water from the immersion in the morning,it only takes about an hour to heat the water and I do not want to have the immersion on the whole night just to get hot water in the morning,the problem with this switch is that it does not have a timer on it,it has a boost timer but that has to be switched on manually which means I have to get up early to switch it on,go back to bed then get up an hour later,is their another solution to this, other than changing the switch?
Thanks again
OK, there are ways of doing what you want - though not with the existing timer. It would be possible with the new one, with some adjustment.

Firstly though, if your tank is well insulated, once it has heated up to the set temperature, it uses far less power to maintain the temperature (when it's not being used) - so you may not save as much as you expect having it only on for 1 hour rather than the 7 - How much will depend on your setup, but it will be a lot less than 6/7th of the total. If you have a smart meter then it might be worth checking.

Factoring in the price of a timer and installation etc, the savings may not pay for the work for a while and good insulation on the tank may be a better investment in terms of saving money.

However, setting that aside, there are a couple of ways of achieving what you want. This assumes you currently have two feeds to the existing timer in at your cupboard, a permanent feed from the normal CU that is always live, and an off peak feed from the off peak CU, that only becomes live at 12-7(ish)

1. Use the new timer you have, using the permanent live feed, to run the lower immersion only for an hour, just before you usually wake up. In this case, the off peak feed in the existing timer will need to be terminated safely but not connected to the new timer as it will not be used.

2. Separate the feeds in the cupboard - and set up a suitable timer on the off peak feed so that it runs for an hour at the time you want, with a simple switch for the "boost" top immersion. The only issue with this is that you'll need a timer that can function with battery backup, as the live feed to it will be off for 17 hours. The benefit is that it can only ever come on at 'cheap rate' times, even if the timer gets out of sync.

There may be other ways, with smart tech, etc. but they are probably more complicated and expensive than the situation demands.

So short answer: The only way of doing what you want is to put in a timer that you can change to come on only for an hour, during the off peak time. It can be done with the new timer you have bought, but if you are at all unsure about the connections and identifying which is which or isolating, then find a local electrician who shouldn't take more than an hour to swap things out properly.
 
OK, there are ways of doing what you want - though not with the existing timer. It would be possible with the new one, with some adjustment.

Firstly though, if your tank is well insulated, once it has heated up to the set temperature, it uses far less power to maintain the temperature (when it's not being used) - so you may not save as much as you expect having it only on for 1 hour rather than the 7 - How much will depend on your setup, but it will be a lot less than 6/7th of the total. If you have a smart meter then it might be worth checking.

Factoring in the price of a timer and installation etc, the savings may not pay for the work for a while and good insulation on the tank may be a better investment in terms of saving money.

However, setting that aside, there are a couple of ways of achieving what you want. This assumes you currently have two feeds to the existing timer in at your cupboard, a permanent feed from the normal CU that is always live, and an off peak feed from the off peak CU, that only becomes live at 12-7(ish)

1. Use the new timer you have, using the permanent live feed, to run the lower immersion only for an hour, just before you usually wake up. In this case, the off peak feed in the existing timer will need to be terminated safely but not connected to the new timer as it will not be used.

2. Separate the feeds in the cupboard - and set up a suitable timer on the off peak feed so that it runs for an hour at the time you want, with a simple switch for the "boost" top immersion. The only issue with this is that you'll need a timer that can function with battery backup, as the live feed to it will be off for 17 hours. The benefit is that it can only ever come on at 'cheap rate' times, even if the timer gets out of sync.

There may be other ways, with smart tech, etc. but they are probably more complicated and expensive than the situation demands.

So short answer: The only way of doing what you want is to put in a timer that you can change to come on only for an hour, during the off peak time. It can be done with the new timer you have bought, but if you are at all unsure about the connections and identifying which is which or isolating, then find a local electrician who shouldn't take more than an hour to swap things out properly.
Once again thanks for your time,I think I will go with getting an electrician to change it over ,I will let you know how I get on,as it is not urgent, I will leave it until this covit is cleared up.
All the best and stay safe.
 
I have a Horstmann Electronic 7 timer switch in my kitchen which is faulty and I want to replace. However, I no longer have Economy 7 or off-peak supply, just standard rate. The timer is only for my immersion hot water heater (3kw) which I want to programme to come on at different times of the day or boost when required. What is the best recommended switch to buy, preferably close to the size of the Horstmann to limit the redecoration required
 
I have a Horstmann Electronic 7 timer switch in my kitchen which is faulty and I want to replace. However, I no longer have Economy 7 or off-peak supply, just standard rate. The timer is only for my immersion hot water heater (3kw) which I want to programme to come on at different times of the day or boost when required. What is the best recommended switch to buy, preferably close to the size of the Horstmann to limit the redecoration required
You may know the Horstmann timer you have, sorry had, can be linked internally (joining terminals 4 & 5) to just operate one immersion with all functions available for the single immersion. Or maybe it's wired like that already.

So buying another Horstmann might be a simple solution (new best price ~ £60)
 
Last edited:
You may know the Horstmann timer you have, sorry had, can be linked internally (joining terminals 4 & 5) to just operate one immersion with all functions then available for the single immersion.

So buying another Horstmann might be a simple solution (best price ~ £60)

The Horstmann I have is designed for use off-peak, which I don’t have. I’m not sure what you mean by one immersion as I only have one immersion heater, but the biggest issue is that the Horstmann only allows me to program one one/off cycle, when I would like multiple on/off cycles at various times in the day. The horstmann was installed when I had an eco7/off-peak option which has since been removed
 
The current Horstmann electronic 7 has three on/off periods per 24 hours, and it's not exclusively for off-peak. If you need more than 3 pre-programmed on periods during the day, I agree you will need a different unit.

A typical hot water arrangement was to have an immersion heater at the bottom of the tank, and another half way up. The bottom one would be using off-peak, and the upper one used for a boost (so you would only ever get half a tank of hot on 'boost').
The Horstmann is designed for the twin immersion situation, but with one immersion you can still use it as a conventional timer.
 
Last edited:
Didn't realize there was 2 types there

A basic boost model with 2 supplies and the timer+boost model

Can you link the outputs on both types for timed/boost control of a single heater, wouldn't be that common a requirement though would it?
 
Last edited:
Didn't realize there was 2 types there

A basic boost model with 2 supplies and the timer+boost model

Can you link the outputs on both types for timed/boost control of a single heater, wouldn't be that common a requirement though would it?

B4A337A0-14F5-4ED5-87C4-E428CC91DFED.jpeg
The "electronic 7" (which I used to have in our property!) has a single supply in, and is configured to drive 2 immersions but ensures that both can't come on at once (obviously!). The instructions include the option to link the off-peak and boost immersion output connections together, so all the features can be available for one immersion.

It may be that GaryMac's timer was an older version than the current model above


The E7BX has separate incoming supplies for off-peak and normal
Ie two supplies (off-peak and day rate) into one single immersion:
12F5029D-E561-45E8-B09A-C1FD34ACCC13.jpeg
55AECC4F-0A05-4871-9CF8-F26CC740257F.png
The Economy 7 Quartz has just one supply input, as per the electronic 7, but seems to be based on 'mechanical' timers:
Used for one supply to feed two different immersion heaters normally.
2525F6BE-D7BC-47C6-B390-743DD5228DF7.jpeg
And the note about linking the outputs holds true for this one as well:
A04FC3EC-3147-4C2A-A2D8-B4A23797528C.png
 
Last edited:
The two controllers you mention are designed to perform slightly different functions.
My understanding is the e7bx you have is connected to both your normal rate daytime supply, and also your cheap rate supply, and provides the ability to manually switch immersions and give a boost function. It does not itself contain a timeswitch but relies on the meter cheap rate timeswitch.
So daytime rate and night rate supplies in, and connections to the immersions out.

The proposed replacement is itself a timeswitch, and can control two immersions, but it only has one permanent supply in.

It depends on your supply and billing arrangements as to the viability of the swap. You would need to connect the new timeswitch to your normal rate supply for the clock to run all the time, so the question is - if you consume power during the cheap rate period from your full rate supply, are you charged at the lower rate? In which case you could wire the new timeswitch thus, and ensure the clock 'on' and 'off' periods are within your suppliers time periods.

Then you will have a live cheap rate supply cable that now has nowhere to go in the new timeswitch!

Sorry for the verbose reply!
Hi Mike-I hope you are well? I'm jumping on this thread because I have a Timeguard timer connected to my water cylinder-this one: 24 Hour/7 Day GP/Immersion Heater Timeswitch - Voltage Free Contacts | Timeguard (NTT04)
Timeguard-Controller.png



Yesterday I had my two rate Economy 9 replaced with a one rate smart meter-I emphasised to EDF and the meter guy that I want them to keep my off peak supply "live" (as opposed to shutting it off) and to feed both meter tails (off peak and peak) in the one rate 24/7 supply. The meter guy seemed to understand and assured me that is what he did, however, when he left, I noticed that the left hand timer (the left = my former off peak supply) & the right timer = 24/7 supply....the red light (indicating powered) was off, on my left timer....the old off peak timer. And so I phoned EDF and they said they will send a technician over as an emergency call...today. I had even checked to see if my water cylinder was heating up at the times I had set the timer to come on-it wasn't. Whereas when I had the two rate supply....it worked fine. However, and strangely, this morning when I checked both timers to see if by some miracle, the red light would come on for the old off peak timer....it was on! And so I assumed problem solved. But I was wrong. Because I checked an hour later and the light is off. To be clear-the red light on the timer on the right, is always on. That suggests it has 24/7 power. But I was of the belief that once I was put on a one rate supply and tariff...that the timer on the left side should also be on 24/7 supply and therefore the red light should always be on.

My electrician is adamant that EDF can fix this on their end-but EDF keep telling me that they don't come into properties to touch anything in here-their work all takes place at the meter.

But having read your reply to the above (original post) here-I'm wondering whether it is my left hand timer that needs re-wiring, and if so, how? I need to communicate this to my electrician. The electrician said this problem can be fixed (if EFD don't fix it) at the fuseboard level....but having read your post-is this merely a case of rewiring how the left hand timer is functioning (at the source/at the timer)? I hope you can advise because I am beside myself that the left hand timer isn't working-that timer is connected to my lower immersion (the immersion that heats up the entire water cylinder) whereas the top immersion is connected to the 24/7 supply, and it only heats up the top of the cylinder. Traditionally, and when I was on Econ 9 that timer/immersion was only used as a "boost" if I ever needed more hot water. I look forward to hearing from you.
 

Attachments

Last edited by a moderator:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Caithness

Thread Information

Title
Immersion heater timer
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
wunatey,
Last reply from
EricMark,
Replies
17
Views
6,683

Advert

Back
Top