Surely an earth resistance tester (the one with the long wires and the T spikes) would be better unless the area around the rod(s) is built up or paved.

This particular installation is a Church surrounded by a tarmacked car park.
Also, to prevent theft of he copper rod, the electrode is contained in a steel tube to a height of approximately 4M.
 
I have only had small involvement in lightning protection, but when I have the requirement was <10ohms to earth from any point on the installation/ <10 ohms from the highest point to earth.
Not an electrode resistance of <10 ohms to earth.
 
I have only had small involvement in lightning protection, but when I have the requirement was <10ohms to earth from any point on the installation/ <10 ohms from the highest point to earth.
Not an electrode resistance of <10 ohms to earth.
That I why I asked for a discussion, there is so much conflicting information out there. I am currently trying to working my way through Megger's "Down to Earth", and thought a discussion may help.
I mentioned to an old hand what I was looking at and he told me remembered doing this with a loop tester.
 
If the building has a single lightning conductor the maximum reading of the rod should be below 10 ohms. We normally do a fall of potential test on a single earth if possible otherwise test off a "known earth" such as a street light or the earth on a plug socket in the building.

Should really be done by a lightning protection company though.

Megger DET3TC is what we use.
 
Last edited:
That I why I asked for a discussion, there is so much conflicting information out there. I am currently trying to working my way through Megger's "Down to Earth", and thought a discussion may help.
I mentioned to an old hand what I was looking at and he told me remembered doing this with a loop tester.

You need to get a copy of the BS for lightning protection and test in accordance with that, not free help guides.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Instrument for Testing a Lightning Conductor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
slingshot2000,
Last reply from
davesparks,
Replies
16
Views
3,438

Advert

Back
Top